It should be realised that the shower does not run flat out all the time only when it is heating at max.
If the cable is clipped direct then as Table 4D1A states the cable is rated at 47 amps.
AS a 10.5kW shower pulls 43.5A and you are using a 45A ocpd then what's the problem with using 6mm?
6mm has a ccc of 47A provided the installation method is C. If it passes through any insulation in the loft, then re-route it so it's on the woodwork in fresh air. Use 4 inch pipe to provide an air space where the cable must pass though the insulation layer.
And you need to follow manufacturers instructions which usually say they want a 10.5kw on a 50a breaker which if 6mm carries 47 amps best case is not good enough so you would need to upgrade to 10mm anyway to adhere to the instructions, and probly for warranty reasons too if anything goes wrong with it in future