still cant get me adibiatic right for this shower.. its a tn-c-s so say max of 0.35 ohms and its 10m max so say 0.45 as calculated zs = 511A
511 x 511 = 261121 x 5 = 1305605 / 115 =11353 and the square root off 11353 = 106 which is wrong.
well its over 32A
perhaps you should look at the trip time graphs in the regs bookwell its over 32A
if i use .4 it still comes out @ 30mm.. its probably the computer calculator
- - - Updated - - -
ok jude, this why i used 200 as this is the limit on 40A breaker
it comes out @ 6mm cpc where 6mm t&e only has 2.5 cpc
))i can see it now jude , i was square rooting everything but now know have to square root then divide by k value.. ty for being patient .... ps mostly domestic so just follow green book so id know 43m is maximum on a 2.5mm cpc
- - - Updated - - -
i did notice jude , that's when i went i am a engineer))