mmm tadpole wellington. makes a change from beef.
still cant get me adibiatic right for this shower.. its a tn-c-s so say max of 0.35 ohms and its 10m max so say 0.45 as calculated zs = 511A
511 x 511 = 261121 x 5 = 1305605 / 115 =11353 and the square root off 11353 = 106 which is wrong.
511 x 511 = 261121
261121 x 0.1 = 26112.1
√26112.1 = 161.6
161.6 ÷ 115 = 1.41mm²
if i use .4 it still comes out @ 30mm.. its probably the computer calculator
- - - Updated - - -
ok jude, this why i used 200 as this is the limit on 40A breaker
- - - Updated - - -
You're thinking about it all wrong. The current that will flow in fault conditions is determined by the Zs of the circuit. It has nothing to do with the Ia of the breaker, this is the minimum value that will cause the breaker to operate in the required time.
i can see it now jude , i was square rooting everything but now know have to square root then divide by k value.. ty for being patient .... ps mostly domestic so just follow green book so id know 43m is maximum on a 2.5mm cpc
- - - Updated - - -
i did notice jude , that's when i went i am a engineer ;)))
- - - Updated - - -
The maximum lengths in the book are more often than not limited by voltage drop and not cpc size or Zs.
I'm a bit confused actually as in the red On-site Guide the max length was 40m which is more or less what I get...
L = (MaxVD x 1000) ÷ (Ib x mV/A/m)
L = (11.5 x 1000) ÷ (40 x 7.3) = 39.38m
Now in the green On-site Guide that value has increased to 43m for some reason