thepurple1

Hi
I would like to fit a 10.5KW shower the mcb is 45Amps
doing a calculation 10.5KW @ 240V= 43.75A
10.5KW @ 230V = 45.65Amps would this be enough over current to cause nuisance tripping on a 45A breaker
 
from the OP, it seems like the MCB is already in place. i read it as a shower replacement . no mention of cable size though. installation method and length of run would determine whether a 6mm would do the job.
 
Hi
I would like to fit a 10.5KW shower the mcb is 45Amps
doing a calculation 10.5KW @ 240V= 43.75A
10.5KW @ 230V = 45.65Amps would this be enough over current to cause nuisance tripping on a 45A breaker

If it's 10.5KW at 240V then it isn't going to be 10.5KW at 230V is it?
I'd suggest you read the spec for the shower again.
 
Hi
I would like to fit a 10.5KW shower the mcb is 45Amps
doing a calculation 10.5KW @ 240V= 43.75A
10.5KW @ 230V = 45.65Amps would this be enough over current to cause nuisance tripping on a 45A breaker
What size cable have you got in? or what size are you intending to put in? Volt drop? Method of installation? Earthing arrangement? Main equipotential bonding? Rcd? Regarding energy saving will a 7.5 kw surfice?
 
Hi
I would like to fit a 10.5KW shower the mcb is 45Amps
doing a calculation 10.5KW @ 240V= 43.75A
10.5KW @ 230V = 45.65Amps would this be enough over current to cause nuisance tripping on a 45A breaker

Gotta say, and I'm sorry to have to put it so bluntly, but never before have I seen such a blatant display of 'fail', never in all my life! Lol

If the shower says 10.5kW at 240V, how on earth is it going to be 10.5kW at 230V???

I suspect given your profession that you're not a moron and that really this is just a brain fart of epic proportions on your part. Don't worry, we all have them, myself included. One thing I would say, in my experience, it always helps to go back to basics!

Ohms law is your friend!
 
What size cable have you got in? or what size are you intending to put in? Volt drop? Method of installation? Earthing arrangement? Main equipotential bonding? Rcd? Regarding energy saving will a 7.5 kw surfice?


Got a 6.9 at our place and its wicked man wicked.

Mind. We do have 6 bar of water pressure hahahahahahahahshahahahshsshshshh


Iapologicse in advance I am doingdry januar y but have the day off
 
Got a 6.9 at our place and its wicked man wicked.

Mind. We do have 6 bar of water pressure hahahahahahahahshahahahshsshshshh


Iapologicse in advance I am doingdry januar y but have the day off

You won't be laughing so much when you're having your hot passionate power shower with yers bird when I sneak round and kill your power.
That's while I've previously locked you in there.
 

Similar threads

S
Replies
0
Views
15
Stu Thomson
S
S
Replies
0
Views
24
Sandy283
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--

Advert

Thread statistics

Created
thepurple1,
Last reply from
Silly Sausage,
Replies
15
Views
2,940

Advert

Back
Top