Afternoon all,
Just thought i would share my afternoon with you all.
so i have 2 x SMA Sunnyboy 1200 inveters both situated outside next to each other(IP rated of course), when i noticed an earth fault today.

Following the manual, i tested the string, + to PE and - to PE, both 0 Volts

So went onto page 59 - testing the varisitor inside.

When I started to loosen the lid of the inverter, a shed load of water came out of the inverter!!

The inverter has never been opened before since receiving it from the wholesaler!!

Ended up drying the inside of the inverter and there you have it, earth fault fixed!

Just a heads up for you all.

V.:banghead:
 
have you spoken to SMA.
If it has leaked once it will leak again.
I would be inclined to drill a drain hole in it.
 
It's normal for a Sunny Boy 1200 to be opened up somewhere between leaving the factory and being commissioned in order to set the language to English on the DIP switches. Sounds like whoever did it didn't put the lid back properly.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SMA Sunny Boy Earth fault / Water penetration
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
VMan,
Last reply from
JulianC,
Replies
8
Views
3,350

Advert

Back
Top