Regarding the OP appdx 15 shows ring and radial sockets on 1.5mm after an FCU, so just going up a few amps to 16A is fine. as everyone else has already said!
 
Such a simple question has turned into a 4 page debate

Im confused as to why people are asking what load is going to be on it and designating it by label etc....

Without doing the calcs the maximum load permissable through a 1.5mm is 19A, so wire it in 1.5mm, regardless of what you plug in to it, DVR or no DVR, kettle or toaster, by fitting a 16a mcb, overload protection will kick in after 16a to protect the cable, i dont see why people have "foggied" the question ?
But will it "kick in" after 16 A vernam? I thought MCBs to BS EN 60898 will take overcurrent to 1.45 times the rated for upto an hour before going.....
 
Lets make it a D type then, just for fun.
 
Why not use a 5A socket, or a 5/10A double pole switch...then no need to get bogged down with 'it don't seem right' issues
 
This is proving to be a good debate however the original question although very open

"can u use 1.5mm cable feeding a single socket from the DB on a 16a breaker?"

I would say has been answer by many - yes

That said we all, (I believe) would use 2.5 for the wiring of any sockets
 
matt12321
You can do what you want.As long it complies too the current IET wiring Regulations.
 
what about 4mm? saves coming back to the board.
 