Discuss Socket & See tester in the UK Electrical Forum area at ElectriciansForums.net
Dannydandan
Evening,
I use a Socket & See tester instrument to provide a means of confirming safe isolation before working on boilers.
Can anyone explain why I am required to press the touch pad at the bottom of the test instrument in order for it to perform a polarity test?
I understand what polarity is and why I'm testing it, but I don't understand what the significance of this pad is i.e., what does me pressing the pad actually do to the test instrument?
I've asked colleagues and trainers but no one can answer this question!
Many thanks,
Dan
Hi Dan, Welcome to the forum.
Edited - removed comment as I pre-empted the wrong kind of tester in my response.
What Socket and See device is it? Doesn't sound like a suitable instrument for safe isolation? Does it comply to GS38?
Thanks,
The socket & see tester is a 2 pole test instrument. It tests for correct voltage, earth loop impedance and polarity.
Secondly, most boiler electrical connections are made via a spur switched socket so there is no means of safely proving electrical isolation unless using proper test equipment. Even if there was a plug this doesn't account for possible 240v on switch live connections.
Anyway, this is to digress, my point is why I have to press the pad. Thanks anyway though...
As DW use an voltage tester, for example Megger dcm 340. Socket an see have there place don't get me wrong, I swear by martindale check plug had them for many decades.
My bad I didn't realise they had expanded their range of the basic plug unit and volt stick, I assume you have a one of these as you question is about the polarity button.
Evening,
Many thanks,
Dan
It appears that the 'Touch Pad' is exactly that. It's not a switch, it's using your body as a (high impedance) ground reference. It can therefore determine whether the incoming supply has been connected correctly. In the case of a TN-C-S supply, where the 'earth' terminal is provided by a connection to the neutral, other methods of determining correct supply polarity wouldn't work as there's no independent ground reference.
Socket and See Documents
Sounds like it works in a similar manner to a neon screwdriver.
Yep,you can get them brighter,at the end of a hard,sweaty day...
The previous Megger TP voltage tester,had a touch pad,at the rear of the handle,which is omitted on the new model.
The voltage <than,>than,seems superfluous,as <203 or >253 could be a problem,or installations where no problem has been noticed.
Reply to Socket & See tester in the UK Electrical Forum area at ElectriciansForums.net
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Hello everyone, I'm a service engineer from Malaysia and come across a simple problem. I work with instrumentation and the problem I face with is...