If there are only 10A and 16A breakers its not correct under ITC-BT 25 of the regs if its a small install there should be Example 25 amp main switch 25A 30ma RCD. 25 A breaker Cooker circuit 6mm cable, 20A breaker 4mm cable (hot water heater) 16A 2.5mm cable breaker Sockets, 16A 2.5mm cable, Sockets, 10 A Lighting circuit 1.5mm cable. there should also be a breaker called an ICP the size of that will depend on the supply contracted. Why does it make you cringe ? better than a ring IMO. The work will need to be tested and a Bolitin issued. Zones apply in both bathrooms and the kitchen as do socket and switch heights. Dont get caught.