Biff, nail on head!
Split concentric is for post DNO termination, concentric pre termination.
Handled and terminated right, its excellent cable. I’d much rather work with a 25mm S/C than the equivalent SWA.
I took a piece of DNO concentric and put a 1KV test on it. It took seven good clouts with a 2Lb hammer for it to even start breaking down. Not very scientific I know, normal test methods for me.
we use split con in my job on street lighting. we get a lot of neutral-earth faults with it. mostly dead shorts. Tend to use SWA as much as possible now on new installs & rewires as we find it a lot more reliable.
the issues i have with its general use in buildings wiring is that the neutral conductors are not afforded the same level of insulation and protection as the live.
Apart from the obvious one of the live being itself 'protected' by N & E, I can't see how that really stacks up? You've a 7 stranded core covered in one layer of insulation, and a N of 7 x singles (or small stranded) all individually wrapped to produce the same csa - so on aggregate that's far more PVC covering the N than the L!
because the insulation covering the neutral strands is a quarter of the thickness of the live core and can be stripped off with a nothing more than a fingernail - ie , its very thin & weak in comparison.
get a piece and strip it as youve never terminated the stuff. ;-)
its a doddle.....
strip back outer pvc and inner clear selophane wrapping to reveal thus.........
View attachment 21198
twist together neutrals into 1 bundle & sleeving over earth strands
heat shrink pvc boot can be inserted over the base of cores if youre feeling flash
and cable entry is nothing more extravagant than an IP stuffing gland & shroud.
;-)
its a doddle.....
strip back outer pvc and inner clear selophane wrapping to reveal thus.........
View attachment 21198
twist together neutrals into 1 bundle & sleeving over earth strands
heat shrink pvc boot can be inserted over the base of cores if youre feeling flash
and cable entry is nothing more extravagant than an IP stuffing gland & shroud.
;-)
its a doddle.....
strip back outer pvc and inner clear selophane wrapping to reveal thus.........
View attachment 21198
twist together neutrals into 1 bundle & sleeving over earth strands
heat shrink pvc boot can be inserted over the base of cores if youre feeling flash
and cable entry is nothing more extravagant than an IP stuffing gland & shroud.
;-)
As i say, most of the final terminations to this type of cable that i've seen, have been a real pig's ear!!
All looks so easy and simple to terminate when shown like this... In reality, in tight locations, and it can be anything but easy and simple. As i say, most of the final terminations to this type of cable that i've seen, have been a real pig's ear!!
Oh and personally i'd never even contemplate using any unarmoured concentric cable in a direct burial installation, only when ducted!!