Why do the wholesalers still sell them when to adhere to the 17th were using dual rcd boards
Thanks a lot interesting.I would have thought RCD on lighting would cause a lot of nuisance tripping low voltage lighting etc,but I must be wrong.I don't do domestic work but as far as I know in Ireland,lighting cct in bathrooms and external lighting now need to be rcd protected,along with sockets and showers which always needed rcd.I think a lot of guys are just fitting a rcbo on every cct.It seems a bit overkill to me,but I'm open to contradiction..
That'll probably come out in the next edition.I don't find lighting nuisance trips RCDs - they normally trip the MCB.
RCBOs are slowly becoming cheaper so I feel that within a few years a 10 way RCBO board will be about £80-£90 which with the benefits of not taking out 5 circuits in the event of a fault will work out better for all.
They just need to give us more head space in CUs
A split load board is a consumer unit normally split in half (but in the same enclosure) if it was a ten way board you would have 2 banks of 5 MCBs, Each set of 5 MCBs would be protected by 1 RCD (so 2 RCDs in total)