spurs

what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way , there will only be one large consumer a water heater .
 
you can take only 1 outlet as a spur from a ring final unless you fit a 13A FCU
 
i got confused when he didn't mention john wayne (spurs).
 
what is maximum amount of spur sockets taken from a main , the main amperage can be changed easily the wiring is 2.5 and a ring main is not possible without a lot of work as this is a large old house which has been wired this way , there will only be one large consumer a water heater .
1 spur per socket on the RFC See Appendix 15 BS 7671
 
As many as you see to be sensible with a 4mm twin and earth spurring off? I could be wrong, I'm not going to the van at this time for the BYB.
 
what he said about what he above said ^^^^^. although 4mm is capable of handling the current in itself, adding several outlets to the same point on the rfc could overload the 2.5mm rfc cable especially if the point was close to one end of the rfc.
 
If you have a ring final circuit then the recommendation is that the number of unfused spurs does not exceed the number of point on the ring. e.g. with ten sockets of the ring a maximum of 10 unfused spurs is recommended. The number of fused spurs is unlimited.
An unfused spur will only supply a single point of use.
In practice you would be looking at the ring loading and ensuring that there were not a concentration of current drawn at one point of the ring.
 