rakooos

Good evening. This is my first post and apologize for my grammar. I need to wire a steam bath shower which has 3500w max 16amp. I know that i need to use rubber 2.5mm cable but not sure what spur i should install. Can i put this on ring circuit ? Many thank for replies.
 
Last edited by a moderator:
It is possible to connect this steam bath shower to a socket ring. I will install it on 13 amp fuse spur. Thanks
 
It is possible to connect this steam bath shower to a socket ring. I will install it on 13 amp fuse spur. Thanks

Refer to post 3 for the answer to this question and it worries me an Electrician suggests putting a load of up to 16amps on a 13amp spur to start with?

Do you not have your Yellow reg's book to hand?

There are no shortcuts here, you need to supply a dedicated circuit for your steam bath/shower.
 
Last edited by a moderator: