Can anybody suggest a reason why I get random RCD trips on a 16amp radial circuit, but MCB/RCD will always reset after around 8 hours. Radial circuit runs about 16 double sockets. Have tried usual unplugging, plus switching off boiler (including unplugging completely), have replaced motorised valve for water/heating. There is no set time of day and trip can occur after 3 weeks or 3 months. It doesn’t coincide with anything switching on or off, bigger appliances like washing machine is on a separate ring circuit 32amp. Never any issues with other circuits coming from consumer unit. MCB has been replaced. Has to be RCD as it resets okay once Sockets MCB is switched off. After 8 hours MCB and RCD will hold again, until next random trip. Seems to point towards something needing to cool down? Component or something similar. But nothing is plugged in or turned on but still RCD trips. It’s not weather related as it happens in any weather or humidity. We did have an issue with small mice but they have gone. RCD is regular 30 mA. Have tried engaging a couple of electricians but they are reluctant to spend time trying to find a fault once the RCD has reset itself. For them to see it tripping they only have a 8 hour window before it’s okay again. There are no outdoor ponds etc. Any thoughts or advice would be greatly received.
 
This is going to be something really weird.
A leaking shower or sink etc,
Water seeping into a socket or junction box which trips the rcd and takes ages to dry out.

I would expect to be able to track it down by insulation testing as the part getting damp will have likely a poor resistance to earth even when not tripping the breaker.
 
Can anybody suggest a reason why I get random RCD trips on a 16amp radial circuit, but MCB/RCD will always reset after around 8 hours. Radial circuit runs about 16 double sockets. Have tried usual unplugging, plus switching off boiler (including unplugging completely), have replaced motorised valve for water/heating. There is no set time of day and trip can occur after 3 weeks or 3 months. It doesn’t coincide with anything switching on or off, bigger appliances like washing machine is on a separate ring circuit 32amp. Never any issues with other circuits coming from consumer unit. MCB has been replaced. Has to be RCD as it resets okay once Sockets MCB is switched off. After 8 hours MCB and RCD will hold again, until next random trip. Seems to point towards something needing to cool down? Component or something similar. But nothing is plugged in or turned on but still RCD trips. It’s not weather related as it happens in any weather or humidity. We did have an issue with small mice but they have gone. RCD is regular 30 mA. Have tried engaging a couple of electricians but they are reluctant to spend time trying to find a fault once the RCD has reset itself. For them to see it tripping they only have a 8 hour window before it’s okay again. There are no outdoor ponds etc. Any thoughts or advice would be greatly received.
Check whether the kitchen sockets are the old BG type (around 7 years old) as I've many a call out for the exact same scenario. If they are BG change them all.
 
This is going to be something really weird.
A leaking shower or sink etc,
Water seeping into a socket or junction box which trips the rcd and takes ages to dry out.

I would expect to be able to track it down by insulation testing as the part getting damp will have likely a poor resistance to earth even when not tripping the breaker.
Thanks so much James for your advice and reply.
 
what results do you get with insulation test at 500v? E-N, E-L, L-N? has to be earth leakage, hence the name!
Thanks for your advice and reply. Following Shajazzi’s earlier advice I looked again at the kitchen sockets. There was an unused double socket behind an air fryer. I noticed that the extraction fan of the air fryer was directly in line with the socket and when I removed the socket and dismantled it, I could see it had grease inside and scorch marks between the live and neutral brass insert bars. To add to this the socket is the polished chrome type so I reckon that a combination of the metal socket warming up due to the warm extracted fan on it, was pulling moisture from the colder wall into the back box, plus the grease moisture extraction from the fan directly into the socket front was causing the short and the RCD to trip. I guess the 7 hour wait before the RCD would reset was due to the greasy moisture drying out inside the socket. Anyway time will tell now that’s it’s been rectified. I’m just glad I found this forum and the great advice.
 