#67 as part of the research I came across recommendations about not putting inverters on RCDs. I suggested this to electrician but he wasn't comfortable with that
 
Hopefully new electrician coming on 15th. I will invite him to comment if he can or cannot resolve it. That will obviously be much more useful than my observations.
I will point him to this thread but would you recommend I ask him any specific questions ? I am not suggesting that as a professional he wouldn't know what to do. Just in case it helps.
 
Is the only reason the A/C set up is protected by RCD as it is due to the type of C.U. you have already.If you do get the C.U. set up changed/reconfigured and the wiring is all surface you may not need the RCD/RCBO element.Do the A/C installers usually put on MCB only.
 
Not sure I understand your questions / comments.

To my simple mind:

Never previously had a single rcd trip. A/C installed by what I believe is reputable experienced company. Almost immediately frequent RCD trips. Could prevent them by isolating A/C both internally and externally. Seemed a no-brainier to me. Called the A/C company who said an electrician should be consulted. Persisted and they sent an engineer who identified the link with the dishwasher circuit.

Since then no-one can work it out and all we have is repeated and sometimes frequent RCD tripping.

I will go with the transfer to all RCBOs if only to avoid disconnection of fridge freezer, internet routers etc.
 
Not sure I understand your questions / comments.

To my simple mind:

Never previously had a single rcd trip. A/C installed by what I believe is reputable experienced company. Almost immediately frequent RCD trips. Could prevent them by isolating A/C both internally and externally. Seemed a no-brainier to me. Called the A/C company who said an electrician should be consulted. Persisted and they sent an engineer who identified the link with the dishwasher circuit.

Since then no-one can work it out and all we have is repeated and sometimes frequent RCD tripping.

I will go with the transfer to all RCBOs if only to avoid disconnection of fridge freezer, internet routers etc.
What I mean is depending how the A/C circuits are installed they may not need RCD/RCBO protection under the regs, but as they type of consumer unit that you have they have had to be installed on one and are adding to the leakage current making it trip.
 
Ok thanks. So does that mean I might be able to get the supply split and put the A/C on a new mini CU?
I would get the A/C wiring tested before you go to the expense of an all RCBO board, or any other expensive moves, seen a lot of A/C electrics thrown in by so called engineers, if it works that's good enough in most cases, how many A/C engineers have you seen with a MFT?
 
I would get the A/C wiring tested before you go to the expense of an all RCBO board, or any other expensive moves, seen a lot of A/C electrics thrown in by so called engineers, if it works that's good enough in most cases, how many A/C engineers have you seen with a MFT?
The absence of an MFT could be why there was no Electrical Installation Certificate provided by the A/C installers (that is if I have read the thread correctly).
I would have expected the A/C engineer to provide a resistance value and which cores of the circuit had faults on, in their report identifying the D/w circuit as the culprit.
 
Engineer report_Page_1.jpg

As you can see (or perhaps not), not a very technical report
 
UPDATE to this perplexing problem. I am grateful to everyone for their time and contributions.

An expert visited a couple of weeks ago. He found that the problem was not over-current, rather accumulated earth leakage - as has been suggested by some above - and a Neutral-Earth fault on the downstairs ring - there was a nicked blue wire in the metal back box of the dishwasher socket.

Additionally and exacerbating, the earth conductors in the kitchen 9 gang DP switch plate (which includes the dishwasher circuit) were not properly connected together and one actually appeared damaged with blackening.

He fixed these faults and then installed 32A RCBOs for the two air con units because there were brief surges in earth leakage when each unit was energised: once energised their earth leakage was small. These brief surges when added to the accumulated earth leakage were detected as excessive by RCD2.

Since this was done we have had no further trips. It has only been two weeks, so I understand it might yet recur, but suffice to say that we have not been able to have both aircon circuits on at the same time for several months so something has definitely changed.

Thanks again to everyone. I am hoping this problem is solved - time will tell.
 
^^ Good man .......... I really appreciate your feedback - so few people do this and its good to hear that it seems to have been resolved.

Dual RCD boards have certainly not helped - with more and more devices in a house adding to "natural" leakage, so a small fault can push an RCD over the limit.
 