I have a very strange repeated RCD tripping scenario, which appears to suggest that two unrelated circuits are connected. Any problem solving thoughts would be appreciated.

I have an electrician who has done several jobs for us (new lighting circuits, appliance installation, outside lights, changing sockets etc). I am very pleased with him, and he has visited around 5-10 times over the last year to try and fix this - but admits he doesnt understand it. He is going to bring in colleagues who specialise in troubleshooting. So we both just thought it might help to put the problem out there for any ideas. I do not touch anything electrical myself.

New build detached house, finished 2012. Dual split load consumer unit with RCD on both (picture). Everything worked fine until last summer when Air COnditioning installed by very experienced professional firm. They installed 5 split units in 5 rooms, and put two outside Mitsubishi units each with new dedicated supply with MCB in CU in two spare slots.

Ever since then we have had intermittent RCD tripping, which my electrician has investigated extensively. Coincidentally we have also replaced all appliances since then with new Miele ones and new Liebherr high end fridge, so unlikely they would be involved.

More recently the RCD repeatedly trips unless the MCB for one of the air con circuits is switched off . Both the electrician and air con company have investigated this - but cannot find a fault with the air con circuit. However my electrician when checking all the possibilities discovered a very strange anomaly. First there is a 6 gang double pole grid switch in the kitchen for isolating various appliances (picture). He found that one of them (for plate warmer) had incorrectly had a simple (light) switch installed - so live and neutral were connected when on. He replaced that and checked all the others.

He then made a discovery which is hard to understand. The RCD immediately and repeatedly trips when the air con MCB is switched on. However it does not trip when air con MCB is on but dishwasher grid switch is off. Turning the dishwasher grid switch on immediately trips the RCD. The air con works fine and no RCD trip when dishwasher isolated, but dishwasher works fine and no RCD trip when air con isolated! We have repeatedly tested and found the same results.

My electrician is seeking advice but does not understand how a new air con supply can somehow be linked to the dishwasher which comes off the ground floor ring mains which has no connection to the air con circuits. Not only has he inspected and tested the CU several times but so have two very senior technicians from the air con company.

This all happens consistently including when all other appliances switched off, so I do not believe the supply is insufficient.

Hope this makes sense. I am not sure if posting pictures is allowed from new members, so I will try to do so in the next post.
 
my thoughts would be that both the dishwasher and the air con have appreciable earth leakage, each on it's own insufficient to trip the RCD, but together take it over the threshold. a ramp test of the RCD to see what it trips at, and an earth leakage clamp meter will help to resolve the problem.
 
Pictures
CU.jpg
Grid.jpg
switch.jpg
 
Thanks both.

Puzzled that professionals havent excluded that.

The dishwasher was replaced during this period. So unlikely both old and new would be faulty in same way? I assume therefore the earth leakage is somewhere in the supply to the socket for the dishwasher?
 
I have Miele appliances and they have never caused problems. Disconnect the air con and see if it persists.
 
pleased with him, and he has visited around 5-10 times over the last year to try and fix this - but admits he doesnt understand it. He is going to bring in colleagues who specialise in troubleshooting.
may be the spark should have found the fault 2 time in ,do you not think so ,
by calling in colleague to trouble shoot for him ,if it was me, I would not have confidence with him with the spark you have now !
 
As the air con circuits are more recent I doubt they are interconnected with any existing circuit. I agree with Tel in #2 that the combined earth leakage of the equipment is tipping the rcd over the edge and this should be investigated as stated in #2.
 
Buzz - I agree. We will be bringing in someone new as well.

Also the air con company who I believe have good reputation, sent their 'most experienced' technician and they denied any problem with air con circuit, which doesnt appear to be consensus above. So that's two independent people who couldnt identify problem.

I am a doctor and we dont have a problem with getting second opinions for difficult cases - but I wont draw parallels between electrical circuits and the human body...
 
I am a doctor and we dont have a problem with getting second opinions for difficult cases - but I wont draw parallels between electrical circuits and the human body...[/QUOTE]

...and like doctors you can get good, bad and inexperienced electricians - you just haven't found a good one yet.

...and the human body is an electrical circuit.
 
He then made a discovery which is hard to understand. The RCD immediately and repeatedly trips when the air con MCB is switched on. However it does not trip when air con MCB is on but dishwasher grid switch is off.

You wrote the above. Is the RCD tripping when:

a. the (offending) a/c MCB is switched on - the other being off?

b. the(offending) a/c MCB is switched on - the other being already on?
 
Borrowed Neutral maybe??? did the A/C guys leave you any testing results or did they just install switch on an then leave.?
if it was that, maybe both RCDs would trip.just thinking aloud. but onlyif the N was fed from the wrong N bar perhaps.
 
I suppose like distance diagnosis/prognosis of electricals/bodies there needs to be schematics and info nothing like being on site. I don't suppose the electrician would care to join us and give further info like his tests or bonding situation etc. etc.???
 
In my humble opinion, if the AC guys had fitted rcbo for their new circuits this problem perhaps would not have occurred or would be obviously AC related. Agree with Various about leakage and possible mixed Ns.
 
Tel, I think Ruston was meaning that it is difficult to give a good diagnosis if basing it on the findings of the OP's spark, who's track record hasn't been 100% so far. Don't think he was aiming it at you.
 
@DPG AND @telectrix I was yes , I can see I abbreviated that too much.
I think Tel is correct if the breakers are wired correctly . The reference to the grid switch could be an influence too.
You have to be there for one like this.
 
Thank you all for the courtesy of your replies and for sharing your expertise.

I never expected a 'remote diagnosis' but the information has been interesting and useful.

I do not think there is anything to be gained by commenting in public on my electrician but I note the opinions. Suffice to say we will be moving on, but he has performed several installations for us which have worked satisfactorily.

While I realise it will not correct any fault, I will probably take the opportunity for the next electrician to fault find but also convert the CU to RCBO's - at least it will make any future faults less intrusive. I have some neighbour's recommendations but would you recommend placing a post on the Find An Electrician forum?
 
In your initial description you wrote 'the mcb' which I highlighted in my post #16. It appears to me from looking at an enlarged image on my CPU screen of your consumer unit, there are two MCBs on the far right which between them supply the 5 split system units. The left of the two feeding a/c systems 3, 4 and 5 and the right of the two a/c systems 1 and 2. Is this correct?

(And I understand from what you wrote you have 5 split systems where each split system comprises of an internal unit(IU) and two external units(EU). Or, do you have 5 internal units and two external units, 3 IUs working with one EU and the other 2 IUs paired with the other EU - to create 2 multi-split a/c systems?).

And I understood that only one of these MCB protected a/c circuits was causing RCD trip problems when interacting with the DW and/or its circuit. I assumed, perhaps wrongly, that the offending mcb was the far right one since it was off.

My post #16 seeks to clarify if the powered up/down state of one of your home's split a/c systems has any effect on whether the other (which I called the offending one) causes the RCD to trip if the DW is not isolated.

Could you also tell me the model number of your EUs and whether they are described as 'inverters'.
 
your present electrician may be a good spark, but fault finding is something that can be difficult for even the most experienced. i know , being biassed towards repairs and faults. some can be baffling to say the least. example is i've had several RCDs fail to trip, even on the test button. each case has been a Neutral fault that has taken up to a few hours to solve, still tink a ramp test and a trace of leakage on both the a/c and appliances is the way to solve your problem.
 
Marconi - thanks.

There are two mcb's on the far right. The left is 3,4,5 and the right is 1,2. (it is the 1,2 which seems to cause a problem).

there are 5 internal units. THe 3 bedrooms go to one external unit, the kitchen/family room and the living room go to the (slightly larger) external unit.

The circuit which appears to cause the problem is the end MCB supplying 1,2 (kitchen & living room). You are correct that is why we keep it off.

THe powered up/down state has no effect. It occurs when they are not on, and frequently has occurred in the middle of the night when also no other appliances are on.

The units are the Mitsubishi Zen R410A inverters. The two external units are slightly different (detailed calcs showed units 1,2 needed larger units). I will get the exact model details shortly.
 
Marconi - from the A/C contract:

To supply, install and commission a comfort cooling system at the agreed location.

We have specifically selected Mitsubishi Electric equipment for this installation. Mitsubishi Electric are widely recognised as leading manufacturers of air conditioning equipment and offer exceptionally high quality engineering coupled with, what experience has taught us, maximum reliability and longevity.

The Inverter driven system offers both cooling and heating functions.

System Specification

Kitchen/Family Room & Media Room (Multi-split system)

1 X 5.0kW Zen Wall Mounted System

1 X 3.5kW Zen Wall Mounted System

Olivia, Francesca & Master Bedrooms (Multi-split system)

3 X 2.5kW Zen Wall Mounted Systems
 
@Op

Tel is righ about earth leakage. Should have used a clamp meter and narrow it down.

Has he ever tried swaping that ac unit mcb which is off with one of the mcbs from another rcd?
 
Are you able to unplug the dishwasher easily? If you can could you do that and then:

Turn off MCB for a/c 1 and 2 and DP switch for DW.

1. then see if with the DW circuit on at the labelled DP switch the RCD trips when you turn on the MCB for a/cs 1 and 2?

Turn off MCB for a/c 1 and 2 and DP switch for DW.

2. now turn on MCB for a/cs 1 and 2 and then turn on DW DP switch.

Turn off MCB for a/c 1 and 2 and DP switch for DW.

3. Turn on MCB for a/c 1 and 2 and leave DP switch for DW off for several hours.

What does RCD do for 1, 2 and 3?

Take care to be around lest you have fridges and freezers supplied by the RCD.
 
Marconi - it's a new miele dishwasher and it's only 4 screws to pull it out. Will be able to do without much difficulty.

I will try as you suggest - will report back and be interested in the results.

Booking a new electrician.

Sparkie - one of the troubleshooting steps previously was to replace the MCB with a new one. It made no difference.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
Strange RCD tripping problem
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
87
Unsolved
--

Advert

Thread statistics

Created
Mjbarnard,
Last reply from
ruston,
Replies
87
Views
14,073

Advert

Back
Top