If we have a double pole RCD which is, let's say 30mA 80A, will it trip in an overload situation above 80A in a similar manner to an 80A incomer? Or is it just 'rated' at 80A in the same way a switch may be rated at 6A or whatever?

I'm sure it's a dumb question that I should know the answer to nut I'm just trying to work out why RCBOs are RCBOs when RCDs have current ratings anyway......
 
Well isn't each rcd and mcb set at a setting above its stated amount like a 32A could hold 33A but for the regs sack they stat a set limit?
 
for a type b its 5xin for auto disconnection (which if you divided by voltage will give you zs without having to look in brb) and 1.45xin for overload.
 
If its rated at 80A thats the maximum safe current it will handle before meltdown.

So if (for what ever reason) more than 80A goes across the device will the meltdown leave the connection open or closed? I was about to ask 'are they designed to go open circuit under these conditions?' but then we're into RCBO territory. So presumably they may be either open or closed depending on the way the meltdown affected it. Would that be a fair assumption?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Stupid question about RCDs
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
rocker,
Last reply from
Notsosmart,
Replies
5
Views
1,525

Advert

Back
Top