Search the forum,

Discuss Sub main 125m in16mm with 80A 1361 over current device in the UK Electrical Forum area at ElectriciansForums.net

My guess without looking up the figures and doing the maths myself is that if it's legit it's probably down to still being able meet disconnection times based on a very low Ze? I'm assuming it's a 90C+ rated cable type.
 
Seems a long run,& on 80 amps.
Wonder what the actual design current is.
Some cable types on the right method are comfortably into three figures on 16mm so it's not impossible (but I'll grant you unlikely!)
 
Sound like someone just looked at the fuse and current-carrying capacity and nievely said "yes gov, that will do".

Plugging in 80A, 125m and a generous 5% drop in to the Doncaster cable calculator suggests 50mm cable...
 
Maybe they don't need 80A, but I really doubt that fuse would meet Zs disconnection at that length. Also if they only needed, say, 40A or so then fusing down to that (or just above) would achieve selectivity with the (presumably) 100A cut-out supply fuse.
 

Reply to Sub main 125m in16mm with 80A 1361 over current device in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock