Have a job where Ze is 0.36 ohms on a TNC-S with 80A BS1361 suppliers fuse. The general rule, as per OSG (page 11), is if Ze is below 0.35 ohms then this is acceptable, but that relates to a 100A fuse (OSG fig 2.1 on page 15 refers). Now I believe that this installation should comply, so have been looking in to the theory behind max Ze to confirm this. The OSG is, after all, only a guide. Please check my thinking below....

This is not a final circuit, therefore 411.3.2.3 should apply, so the allowable disconnection time must not exceed 5 seconds
Appendix 3 Figure 3.1 'Fuses to BS 1361' shows that a current of 460A is required to disconnect a 80A fuse in 5 seconds.
Ohm's law V=IR can be rearranged as R = V/I
R = 230 / 460 = 0.5
So for a 80A BS1361 fuse to disconnect in a time not exceeding 5 seconds then the Ze needs to be 0.5 ohms or less
Therefore my measured Ze of 0.36 ohms complies

Is this correct?
 
souds logical to me. however, can you be sure that your meter is accurate to 0.01 ohms?
 
That works both ways Tel, so if I had measured 0.35 ohms (the supposed top limit) could I then be sure that it wasn't really 0.36 ohms? As it is, if the max Ze in this case is in fact 0.5 ohms then I am comfortably inside that. But it is good to know that I am not barking up the wrong tree.
 
it is a bit high fot TNC-S though usually get a reading of 0.2 or less. possible slack connection on tails?
 
It seems correct, however, please remember BS7671 does not apply to the DNO equipment and installations.
The fundamental science however does, so your example is correct in that aspect.
 
Have a job where Ze is 0.36 ohms on a TNC-S with 80A BS1361 suppliers fuse. The general rule, as per OSG (page 11), is if Ze is below 0.35 ohms then this is acceptable, but that relates to a 100A fuse (OSG fig 2.1 on page 15 refers). Now I believe that this installation should comply, so have been looking in to the theory behind max Ze to confirm this. The OSG is, after all, only a guide. Please check my thinking below....

This is not a final circuit, therefore 411.3.2.3 should apply, so the allowable disconnection time must not exceed 5 seconds
Appendix 3 Figure 3.1 'Fuses to BS 1361' shows that a current of 460A is required to disconnect a 80A fuse in 5 seconds.
Ohm's law V=IR can be rearranged as R = V/I
R = 230 / 460 = 0.5
So for a 80A BS1361 fuse to disconnect in a time not exceeding 5 seconds then the Ze needs to be 0.5 ohms or less
Therefore my measured Ze of 0.36 ohms complies

Is this correct?

Yes it is correct.If the supply was 100A the max would be about 4Ω .
This is why often the DNO, will refuse to allow TN-S supplies above 60A, or will stipulate that an upfront RCD is required, or even that the supply must be changed to TN-C-S.
 
silly me i didnt remember but thanks for the correction spinlondon. i need to look and keep quiet me thinks
 
silly me i didnt remember but thanks for the correction spinlondon. i need to look and keep quiet me thinks
No not really.
To my mind, if you don't question, you don't learn.
Also, anyone who makes any statement, should be able to explain their reasoning behind the statement.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Peterborough

Thread Information

Title
Supplier's fuse, disconnection time and max Ze
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
ringer,
Last reply from
Deleted member 26818,
Replies
9
Views
13,397

Advert

Back
Top