Hi All

Customer has built a guest house in his garden (log cabin style) and called me to install c/u etc. Problem is this: house has a 100amp supply. house has 9.5kw shower, electric oven plus usual appliances. Garden guest house has......8.5kw shower, electric oven plus other appliances.
I have told him that the best option is to get EDF to install a seperate supply for the garden house - only other option is to run a submain in 25mm SWA from house c/u on a 63a mcb. Problem is, as I have pointed out, if both showers and both ovens are being used (plus other appliances) he's going to exceed his 100amps and trip the main switch.
Anyone got any suggestions - and anyone have any idea how much EDF would charge to install a seperate supply?

Cheers
Andy
 
Do a diversity calculation you will probably be OK running your 25mm etc. I have a HMO with 3 showers and no problems 3 years on.

Regards.............Howard
 
Does it have planning permission ? If so, with all that load, would you want the guests to blow the main fuse for everything. If a separate building for accomodation, it surely should have a unique supply.

Not a great scenario here. Limit the guest house to 40A ( 16mm SWA ). Put in a smaller MCB for the hugely over-rated shower, like a 32A. How often does a shower user require all 9,5kW to be in use ? Better to inconvenience them than the main household.

Another supply would be mega bucks.
 