Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks
 
One good fart after all that popcorn with ears like that mate and you'll clear Everest without touching land fgs !!
 
Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks

Who told you that?
 
wow.this went downhill rapidly!

after the 50th shed supply thread in the last 7 days with not a single poster bothering to use the topic search function , i can safely speak for the forum in saying....
we dont give a sh**.
;-)
 
Whats needed is some aluminium framed greenhouse queries with paraffin heaters in them.

Q.
Do I bond the frame to the nearest wet tree?

A.
Why the fXZ! do you need to bond it?

Or similar scenarios:)
 
Whats needed is some aluminium framed greenhouse queries with paraffin heaters in them.

Q.
Do I bond the frame to the nearest wet tree?

A.
Why the fXZ! do you need to bond it?

Or similar scenarios:)

Good question well phrased, however I do not know the answer to this question just now. But I will speak to the knights who say Ni for clarification on shrubberys.
 
Evening

I am supplying a garage which is 14 meters from the house (House is TNCS), I will be taking the supply from a non - RCD protected 32A MCB using 6mm SWA cable buried. I will not be exporting the earth, so will installing earth rod - TT at the Garage, protected with a 30ma RCD and 2 MCB's 6 & 16amp.

Is is this sufficient protection MCB & SWA or is RCD protection needed?

Where I am confused is the earthing connections from the house as I am not exporting the earth is my only earth connection for the circuit from the earth tag of the SWA.

Also in the garage, I have my earth from the rod connected and the terminal and the earth tag from the SWA.

I originally purchased 3 core SWA and was told I should connect the earth to the house and leave it disconnected at the shed.

Think I have over thought this job and I "cant see the wood from the trees", so hoping for some clarity.

Thanks

Seems you believe everything your told, including leaving a perfectly good earth (0.35 ohm) behind, in favour of an unstable 200 ohm earth!! Good luck to you!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Supplying garage with power
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
Paul Willoughby,
Last reply from
shocking_eg,
Replies
18
Views
2,160

Advert

Back
Top