If this cable run is just passing through the plant room (which is basically the school boiler room when all said and done) Then run whatever cable system you choose, (eg, FP 200, etc...) through a galv' metal conduit within that room.


Personally, i would probably choose a metal containment system or MICC installation for the circuit as a whole, but it seems these day's, both of these types of once mainstay electrical installations, are fast being cast aside in favour of easy fix wiring systems, like T&E, FP 200, and SY... MICC is already virtually classed as a ''specialist wiring system'', how long it's going to be, before the same can be said for metal containment systems is anybodies guess!! lol!!
 
OK, I think some common sense needs to be applied here.

Firstly, this is a plant room in a commercial or state owned building, therefore running mains voltage cable without mechanical protection is simply not acceptable, even if this is run on tray or basket it should be WHITE FP as a minimum.

If there are FP's already installed have you determined what they are for, it is likely at least one will be the fire protection system and as such you must not use FP200 or any other RED coloured cable and you must not run right beside it regardless.

If this is a 3m straight run I would advocate that surface mounted Galv Conduit be used as a "sleeve" to provide mechanical protection to whichever cable you choose to use, T&E utilising the conduit as a sleeve is acceptable. However being a local authority building (I guess as it's a school) I would suggest you use "Hospital" saddles and not spacer bar saddles because most authorities specify Hospital saddles as a matter of course.
 
OK, I think some common sense needs to be applied here.

Firstly, this is a plant room in a commercial or state owned building, therefore running mains voltage cable without mechanical protection is simply not acceptable, even if this is run on tray or basket it should be WHITE FP as a minimum.

If there are FP's already installed have you determined what they are for, it is likely at least one will be the fire protection system and as such you must not use FP200 or any other RED coloured cable and you must not run right beside it regardless.

If this is a 3m straight run I would advocate that surface mounted Galv Conduit be used as a "sleeve" to provide mechanical protection to whichever cable you choose to use, T&E utilising the conduit as a sleeve is acceptable. However being a local authority building (I guess as it's a school) I would suggest you use "Hospital" saddles and not spacer bar saddles because most authorities specify Hospital saddles as a matter of course.

can you add a pic of hospital sadles?

just use normal spacer bar sadles and worked in 5 hospitals and 1 was a new building and spacer bar were fine
 
Re: Surface mount T&E through plant room ?

Distance saddles are usually excepted instead of hospital saddles nowadays...........

- - - Updated - - -

spacer bar saddles a no no no ............
 