OK, I think some common sense needs to be applied here.
Firstly, this is a plant room in a commercial or state owned building, therefore running mains voltage cable without mechanical protection is simply not acceptable, even if this is run on tray or basket it should be WHITE FP as a minimum.
If there are FP's already installed have you determined what they are for, it is likely at least one will be the fire protection system and as such you must not use FP200 or any other RED coloured cable and you must not run right beside it regardless.
If this is a 3m straight run I would advocate that surface mounted Galv Conduit be used as a "sleeve" to provide mechanical protection to whichever cable you choose to use, T&E utilising the conduit as a sleeve is acceptable. However being a local authority building (I guess as it's a school) I would suggest you use "Hospital" saddles and not spacer bar saddles because most authorities specify Hospital saddles as a matter of course.