M
martynb01132
Hi all looking for help on this one, if Im running SWA cables what is the minimum line size before I have to run a seprate earth, cheers Martyn
i would question the kind of company you work for as they are clearly wrong in saying this you can work it out from the calculations in the regs as as i said before its size and core dependant but as you get to the larger swa cables then it becomes a requirement all the time im sure someone else will direct you to the table i spoke of.Cheers I working for a company who insist we dont need to run a separate earth on any swa cable from 10mm upwards I think we do, generally the voltage is 400v 3 line supplies.
the answer is in one of the NICEIC newsletters that are available from their site, I cant remember off hand but I think it was ok to use the armour as the CPC for line less than 6mm. Check the article though
You can go a lot higher than that, just trying to find it on the web and if find it i will post it
Found it
steel wire armour as the earth conductor | GadSolutions,Electrical services,testing and excellence.