Does the OSG quote a Regulation for that.
No, only obliquely by referring to the requirement to use BS/harmonised standards cabling.
What reason would you use them other than shielded control cable when in the proximity of high frequency power cables?
The most obvious, and probably most widely used member of the *Y family of cables would be NYY-J, which has a plethora of uses.
The post I was responding to did not reference shielded control cables, but the *Y family of cables and went on to suggest HO5/HO7 as more suitable alternatives - neither of which are shielded.
Edit: In answer to your question; I don't design installations and simply work to the provided spec and often a BMS or EMS panel will have a small number of shielded control cables carrying 240V. Getting back to SY cable, while it could be argued that its 300V/500V rating allows for installation alongside cables carrying mains voltage, I'd contend that 16mm SY is unlikely to be intended solely for use with ELV.
This is an interesting topic which has digressed from the original point to whether the "Y" cable family should be used or not. In an attempt to add to the debate here is my contribution, ( a little long but as brief as I can).
Part One of the Regs is a good place to start
Regulation 133.1.1 states:- "Every item of equipment shall comply with the appropriate British or Harmonized Standard. In the absence of such a standard, reference shall be made to the appropriate International (IEC) standard or the appropriate standard of another country"
Regulation 133.1.3 states: - "Where equipment to be used is not in accordance with Regulation 133.1.1 or is used outside the scope of its standard, the designer or other person responsible for specifying shall confirm that the equipment provides at least the same degree of safety as that afforded by compliance with the Regulations".
Regulation 133.5 (New materials and inventions) states that "Where the use of a new material or invention leads to departures from the Regulations, the resulting degree of safety of the installation shall be not less than that obtained by compliance with the Regulations. Such use is to be noted on the Electrical Installation Certificate specified in Part 6.
As Eland Cables state compliance with British and European performance test standards, these regulations basically allow its use and the designer (which could be the installer) needs to confirm on the certification documentation.
However as this type of cable has been manufactured for flexible control cables, designed for measurement and control in equipment careful consideration should be given before use as fixed installation power cables.
There has also been comments made about the braiding on this type of cable. Unlike SWA cables the braiding is for screening purposes only and should not be used as a CPC. Using the correct glands will ensure that this braiding is connected to earth. The cpc of this type of cable should be a core conductor coloured green and yellow.
Now going back to the original question by Lozarus regarding coding. Coding can be another big debate but I always ask myself two questions. Is there an immediate risk of electric shock (open live parts) if not it can not be code C1. Is there a risk of shock if a fault/failure occurs again if not it can be code C2 . That now leaves us with a code C3 to use.
Therefore I feel that use use of this type of cable can only be C3
The use of SY cable is "discouraged" within BS7671:2018+A2 2022 On Site Guide Section 7.9, as generally it is not manufactured to a British or Harmonized standard.
It is not rated for external use or for use in ducts. It's normally classed as a control cable rather than a power cable.
On an EICR it should be recorded as a non-compliance.
Reactions: Fazz711
NICEIC recommend C3 on an EICR just for use of SY
I dont understand why it is so popular, i have even seen it used on a 350KVA generator for power.
Its horrible, whenever you touch the screen, which i would only earth one end anyway, its expensive for what it is and there are better cables for all the uses we come across. I think its toughness is an illusion and its outdoor performance is shocking. However, unless it has damage, i would C3 it as there are better products out there, that will last and perform better under most circumstance
Depending on the size of the company, ie, has a H&S department or H&S. I'd just use the phrase that's it's not compliant with BS standards and insurance would likely not cover any incident arising from its failure. Whether that 2nd part of the statement is true or not I wouldn't know. But it may start the conversations along the lines if "what if he's correct and we have a fire or death".
My last company with 30,000+ employees would have started a switch out programme on a phrase like that. Quite proactive to be fair to them. One guy cut himself badly stripping a cable with an electricians knife, next week they were banned and a bunch of new bespoke tools appeared that couldn't get you.
Depends on the company you work for I guess. I'd emphasise the poor workmanship items over the construction of the cable in conversation. Like the glanding, poor terminations, etc. and back it up with a mention of the outdoor cable being close to failing being non BS approved.
Warwickshire
Other
If other, please explain
Estate Manager with Electrical Bias
Business Name
n/a
SY cable on EICR again ....
lozarus,
KungFuTurkeyLeg,