SY cable screen does NOT require earthing although it is considered good practice to do so. If terminated using PVC glands correctly it would not be classed as an exposed conductive part contrary to what you might hear others on here say.
Can you explain why it is not an exposed conductive part, is it because it is enclosed in the sheath?
 
Because there is insulation and then a sheath between the live conductors and the braiding. It would be impossible for the screen to become live under single fault conditions unless earthed using metal glands, in which case it would then become an exposed conductive part. Believe it or not SWA is the same, the only thing that makes the armour of SWA an exposed conductive part is the metal glands used to earth it.
 
no-one ever relies on a braiding as a cpc
whereas swa can provide the sole and only means of earthing.
maybe another way of looking at it :-D
 
Because there is insulation and then a sheath between the live conductors and the braiding. It would be impossible for the screen to become live under single fault conditions unless earthed using metal glands, in which case it would then become an exposed conductive part. Believe it or not SWA is the same, the only thing that makes the armour of SWA an exposed conductive part is the metal glands used to earth it.


Really?

So if SWA was just terminated with plastic compression glands, thats not a problem?...


I wouldn't think to do it, just theoretical...
 
Yeah, theoretically speaking, if there was no way for the armour to become live under single fault conditions then there would be no need to earth it.

It would obviously beg the question; 'Why use SWA in the first place?'. It is also easier to earth it than it would be not to, but technically speaking the armour only becomes an exposed conductive part when we gland it in brass.
 
But surely if the SWA had become penetrated, one of the line conductors say shorted to the armour, which wasn't earthed, that's a dangerous situation....
 
This thread is getting a bit silly now, when sparks use SY or SWA in industrial situations or many others in fact there is a high likelihood of the outer sheath getting damaged due to welders/pipe fitter or many other trades during the installation process thus exposing the armour or screen (not always causing a fault that can be detected on testing / commissioning) so it is always the case IMO to earth as the norm even when people continue to use SY for power as opposed to control its even more important!
 
If SY is being used in areas where it is prone to wear and damage then the wrong cable has been selected for the job in the first place! This also applies if SY is being used for power, however, I stand by what I say. SY braiding does NOT need to be earthed and there is no requirement for doing so and neither does SWA unless stipulated under certain conditions.

That said, I always earth SWA and 9 times out of 10 earth the braiding on SY (albeit not for fault protection but for interference reasons).

The answer to the OP's question is NO, SY screen does NOT need to be earthed. Upon a correct answer being given, only then is the time to have a discussion about the pros and cons of earthing or not earthing it.
 
Not if you can't touch the armour and there is nothing metallic connected to it..
A big can of worms here.... you are so misguided in your thinking ...the braiding when used in LV power power cables affords extra abrasion resistance as does the armour in SWA but in using it for such you must ALWAYS earth it as any damage afforded the the cable could make either the braiding live in SY or the armour in SWA... it is earthed because the cable is rough service hence expected it may be prone to damage thus regardless of glanding the braiding or armour must be earth ---this saves lives, the argument here should be the use of SY as a rough service flex which is a use its not designed for and some manufacturers recommend you dont.

Im surprised at the latest post by you making such statements .... ensuring the armour is isolated from earth is no reason to suggest it can be unearthed in theory ....clearly your forgetting why it is there - if its not used as a functional earth in the case of a SWA then its serves as mechanical protection.

Just got visions of roadworks having diggers go through an SWA without earthed armour because the ends were sealed ....in effect if it dosn't kill the driver as he gets out because his cabs live then maybe the next worker in the pit who stands in the water!!!....... yes i appreciate you said in theory but think about it before posting.

Any metal sheath, armour or braid that is there for mechanical protection should be earthed this has nothing to do with exposed conductive parts.
 
Last edited by a moderator:
If you read the OP the application he is using it for it is a must he earths it and not for you the give him the impression it's not required, I agree HE IS USING THE WRONG CABLE but you should of told him that and not lead him to think he doesn't need to bother because some one on here is telling it doesn't require earthing. IT DOES IN THIS CASE
If SY is being used in areas where it is prone to wear and damage then the wrong cable has been selected for the job in the first place! This also applies if SY is being used for power, however, I stand by what I say. SY braiding does NOT need to be earthed and there is no requirement for doing so and neither does SWA unless stipulated under certain conditions.

That said, I always earth SWA and 9 times out of 10 earth the braiding on SY (albeit not for fault protection but for interference reasons).

The answer to the OP's question is NO, SY screen does NOT need to be earthed. Upon a correct answer being given, only then is the time to have a discussion about the pros and cons of earthing or not earthing it.
 
Well put
A big can of worms here.... you are so misguided in your thinking ...the braiding when used in LV power power cables affords extra abrasion resistance as does the armour in SWA but in using it for such you must ALWAYS earth it as any damage afforded the the cable could make either the braiding live in SY or the armour in SWA... it is earthed because the cable is rough service hence expected it may be prone to damage thus regardless of glanding the braiding or armour must be earth ---this saves lives, the argument here should be the use of SY as a rough service flex which is a use its not designed for and some manufacturers recommend you dont.

Im surprised at the latest post by you making such statements .... ensuring the armour is isolated from earth is no reason to suggest it can be unearthed in theory ....clearly your forgetting why it is there - if its not used as a functional earth in the case of a SWA.

Just got visions of roadworks having diggers go through an SWA without earthed armour because the ends were sealed ....in effect if it dosn't kill the driver as he gets out because his cabs live then maybe the next worker in the pit who stands in the water!!!....... yes i appreciate you said in theory but think about it before posting.

- - - Updated - - -

THE END lol
 
A big can of worms here.... you are so misguided in your thinking ...the braiding when used in LV power power cables affords extra abrasion resistance as does the armour in SWA but in using it for such you must ALWAYS earth it as any damage afforded the the cable could make either the braiding live in SY or the armour in SWA... it is earthed because the cable is rough service hence expected it may be prone to damage thus regardless of glanding the braiding or armour must be earth ---this saves lives, the argument here should be the use of SY as a rough service flex which is a use its not designed for and some manufacturers recommend you dont.

Im surprised at the latest post by you making such statements .... ensuring the armour is isolated from earth is no reason to suggest it can be unearthed in theory ....clearly your forgetting why it is there - if its not used as a functional earth in the case of a SWA then its serves as mechanical protection.

Just got visions of roadworks having diggers go through an SWA without earthed armour because the ends were sealed ....in effect if it dosn't kill the driver as he gets out because his cabs live then maybe the next worker in the pit who stands in the water!!!....... yes i appreciate you said in theory but think about it before posting.

You're missing the point, and I think while you were writing that I answered half of your concerns in my reply to KAS. In response to your last point, the regs call for cables buried under ground to have an earthed metallinc sheath for that very reason. My comment about the armour in SWA not being an exposed conductive part was purely trivia, it wasn't meant to incinuate that not earthing it is the right thing to do. I was using this as a means to demonstrate a factual point, nothing more.

I go back to my main point, SY cable screening isn't designed to carry fault current, therefore it cannot be relied upon to provide fault protection to the cable. It does NOT need earthing. If you are using SY in an area where damage may occur then you are using the wrong cable.
 
Didn't he say he sleeved a core for earth therefore its not used for fault current is it not, so IMO to leave it un-earthed for his situation feeding a boiler WAS THE WRONG ADVICE
 
If you read the OP the application he is using it for it is a must he earths it and not for you the give him the impression it's not required, I agree HE IS USING THE WRONG CABLE but you should of told him that and not lead him to think he doesn't need to bother because some one on here is telling it doesn't require earthing. IT DOES IN THIS CASE

Rubbish! In the manner he is using the SY it absolutely does NOT need earthing! If I could happily use standard flex for a purpose but chose to use SY purely for asthetic reasons I wouldn't earth it. A complete waste of time and money!
 