What if I just strip the braiding off the 10" of cable I used and call it a flexible cable?

Would that bring this 4 page epic to an end??? lol
 
agree. not earthing the brais on SY is like sailing your boat on the open sea without fitting the bung in the bilge.
 
We use a lot of SY cable for power and always use EMC cable glands (mainly from RS). You are going to gland the cable anyhow so you might as well spend a bit extra and call up EMC glands.
The manufacturer of the cable has also stated that their cables can be used for power cables.


Any chance of showing that statement Spoon. I bet there is conditions attached??
 
if you're going to stamp on it, i'd recommend using SWA. :21:
 
Any chance of showing that statement Spoon. I bet there is conditions attached??

I cant find the email from Eland cables, but I did find this from our supplier who contacted them.

I have just had a word with Eland technical and they have indicated that SY cable is not suitable to be used where the main electricity supplier normally terminates their cable ( normally steel wire armoured ) ie between the main incoming power supply and the disribution board.
They have also indicated that it may be used from a distribution board to any application it feeds providing the correct size conductor / fuse is used.
In a nutshell it cannot be used where steel wire armoured cable would otherwise be used.

Yes, Eng54 there are conditions attached.
​
 
So in a nutshell, I'll stick to earthing the braid as I've always done and it seems the most experienced of sparks would as well, also use flex where require and not SY because it looks good, if it's a case of "sling a bit of SY in as that's all we've got" then earth the braid at least lol
 
So in a nutshell, I'll stick to earthing the braid as I've always done and it seems the most experienced of sparks would as well

Most 'experienced' sparks who earth their SY braids 9 times out of ten would know that when a question is asked such as; "Is it a requirement to earth the screening on SY cable?" The answer is no!

Best practice and requirement are two entirely different things, a point I seem to have to stress here on a REGULAR basis!

The OP's question has been answered I believe, and as for the sly digs and ridicule for suggesting something hypothetical, a little controversial but entirely accurate, I've no more time for it. Enjoy the rest of your rants.
 
The below quote is from gn8 2nd edition for clarity on swa and what i go by

"9.3.5 Termination of armoured cables
It is of paramount importance that armoured cables are terminated in a proper manner and in accordance with the manufacturer’s installation instructions. BS 7671 demands the preservation of continuity of protective conductors and specifically requires such conductors to be protected against:
f mechanical damage and vibration f chemical deterioration and corrosion f heating effects f electrodynamic effects (i.e. mechanical forces generally associated with fault
currents).
Even where the armouring is not serving as a CPC, it will still need to be earthed as it is an exposed-conductive-part. Armouring is therefore always to be protected against the above detrimental influences and any other stresses which could impair its continuity. Electrical joints such as those between armouring, cable glands and earthing terminals, are required to be soundly made (mechanically and electrically), and, where necessary, suitably protected.
Regulation 8 of the Electricity at Work Regulations places an absolute requirement on protective conductor connections to earth and states:
... a conductor shall be regarded as earthed when it is connected to the general mass of earth by conductors of sufficient strength and current-carrying capability to discharge electrical energy to earth.
Being an absolute requirement, compliance must be achieved regardless of cost or any other consideration."
 
Last edited by a moderator:
The below quote is from gn8 2nd edition for clarity on swa and what i go by

"9.3.5 Termination of armoured cables
It is of paramount importance that armoured cables are terminated in a proper manner and in accordance with the manufacturer’s installation instructions. BS 7671 demands the preservation of continuity of protective conductors and specifically requires such conductors to be protected against:
f mechanical damage and vibration f chemical deterioration and corrosion f heating effects f electrodynamic effects (i.e. mechanical forces generally associated with fault
currents).
Even where the armouring is not serving as a CPC, it will still need to be earthed as it is an exposed-conductive-part. Armouring is therefore always to be protected against the above detrimental influences and any other stresses which could impair its continuity. Electrical joints such as those between armouring, cable glands and earthing terminals, are required to be soundly made (mechanically and electrically), and, where necessary, suitably protected.
Regulation 8 of the Electricity at Work Regulations places an absolute requirement on protective conductor connections to earth and states:
... a conductor shall be regarded as earthed when it is connected to the general mass of earth by conductors of sufficient strength and current-carrying capability to discharge electrical energy to earth.
Being an absolute requirement, compliance must be achieved regardless of cost or any other consideration."

its not an armouring in sy cable its a screen. not covered by this extract
 
I know
I was referring to previous posts about swa not requiring to be earthed.

That said I still believe sy needs to be earthed
 
Last edited by a moderator:
Most 'experienced' sparks who earth their SY braids 9 times out of ten would know that when a question is asked such as; "Is it a requirement to earth the screening on SY cable?" The answer is no!

Best practice and requirement are two entirely different things, a point I seem to have to stress here on a REGULAR basis!

The OP's question has been answered I believe, and as for the sly digs and ridicule for suggesting something hypothetical, a little controversial but entirely accurate, I've no more time for it. Enjoy the rest of your rants.

We live in an industry where new developement, practices and technology constantly change so as for SY which in most cases is been used for a function to which it wasn't originally designed thus regulations have to catch up, think of the new section within the 17thh that were absent from the 16th but there is an overlap period where what you may be doing has little or no direct regulation regarding it, in these circumstances you need to make that judgement call and however you look at SY if using LV through it it always will require the braiding to be earthed ..... whether you use the terminology 'requirement' or 'recommended' its a matter of the obvious dangers that could exist from not doing so .... the regulations are ever evolving and always playing catch-up.

Also SY has a specifically designed gland for its termination that would make it exposed metalwork now if you were to utilise other glands that lose a specific function of the earthing of the original gland then its down to you to make steps to re-establish the earthing lost by say using a standard stuffing gland....

People are using SY for purposes other then originally designed
people are using glands not designed for use with SY

If you do either of the above you need to know the cable is suitable for the alternative use and that any other functions the correct glands performed other than giving a cable entry/clamp will be still achieved by other suitable methods.

This is why we can't quote a specific regulation for this situation but the more it migrates to other users the more chance we will see it included in the next amendments or even 18th edition.

Until then its common sense to earth the braiding and judging by what i find on site there is a massive lack of it, yes i know its not specifically a direct requirement but other broader regulations do cover the fact that it poses a danger if unearthed.

So 10/10 times when used with LV power i say it is required to be earthed.

PS i know you are not saying dont earth it and see your angle but it may misguide the less experienced in the industry by stating its not a requirement without expanding on that.
 
Last edited by a moderator:
Technically speaking, GN8 is wrong. Look up the definition of an exposed conductive part in the regs.

Im still leaning towards the exposed conductive part.
This is the great thing about this forum it gets people thinking out of the box.
i have the iet tech email i think i will email the link and get there take on it ( the earthing of swa) and post it up
 