Deleted member 26818
The earth conductor is chosen to be able to withstand the expected earth fault current, for the time it takes for the protective device to operate.
Generally the higher the current, the larger the CSA. i.e. an installation with a 100A main fuse, will require a larger CSA earth conductor than that required for an installation with a 60A main fuse.
TT installations, have such a high Ze/Ra, that the fault current is very low. So low that even a 1mm² earth conductor may well be able to withstand the fault current.
The resistance of a 2.5mm² conductor per meter, is just under seven and a half thousndths of an ohm, and the resistance per meter of a 6mm² conductor is just over three thousandths of an ohm.
If you had a measured Ze of 50.457Ω, using a meter of 2.5mm² cable, changing to 6mm² would alter your measurement to 50.453Ω.
If you really went to town, and used 25mm² cable you could get the measurement down to 50.450Ω.