FrighteningI agree. We test a lot of steel shipping containers and they are almost never done correctly. Usually connected to a PME earth is the issue.
FrighteningI agree. We test a lot of steel shipping containers and they are almost never done correctly. Usually connected to a PME earth is the issue.
Yea,agreeA transportable unit connected to a TNS earth will not need an earth electrode or to be under supervision.
The only thing would be if it would be realistic,especially Main Earth bonding,concerning the size of the neutral on a tncsAny transportable unit will need an earth electrode installed unless it is under the supervision of 'skilled or instructed person(s)' in which case the PME can be used.
Construction sites also need to comply with Section 704 as well as 717.
Oh, thank you for spending the time to find that for me. so I have a get out of jail free card if I use the cable and they damage it. I'm usually always overly cautious with these things and thinking what if !!Section 717 mobile or transportable units -
717.52 Wiring systems
717.52.1 Where the supply to the unit is by means of a plug and socket outlet, flexible cables in accordance with H07RN-F (BS EN 50525-2-21), or cables of equivalent design, shall be used for connecting the unit to the supply.
You're welcomeOh, thank you for spending the time to find that for me. so I have a get out of jail free card if I use the cable and they damage it. I'm usually always overly cautious with these things and thinking what if !!
Really H07RN-F is pretty tough, if you need more intrinsic protection then it is really SWA and that is not suited for anything that moves more than very occasionally.I have a get out of jail free card if I use the cable and they damage it.