I don't particularly see the point in L-N IR and it involves a lot of messing about with light switches, lamps, isolators etc.
I dont do the full ring circuit R1+R2 on either C/U changes or new installs. End to end continuity on the 3 conductors is good enough for me and provides me with a pretty accurate R1+R2 reading.

Bad pratice IMHO.
 
I frequently find that doing anything more than basic testing before removing the old CU isn't practical. By the time you've sorted out the rat's nest enough to work out what's what and which circuits are which the only thing left connected are the four screws holding it to the wall!
 
I won't lose any sleep over it
David...
initial verification inspection & testing is clear:
(R1 R2) at every point on the installation...if you dont do this...you are not testing it properly as you will be energising the install before proving polarity/presence of a means of earthing to accessories if using Zs alone...
 