Discuss Testing issues ! in the UK Electrical Forum area at ElectriciansForums.net
Soulsurfer
long story short, Pre-rip out test really old install, TN-S,16mm tails, 6mm main earth !
Ze was 0.22 ohms and 1.2kA fault current.
DNO been up this morning to connect new tails 25mm I supplied through switch fuse and 16mm earth. Fit board new, go to check Ze and get 0.00 ohms ! PEFC 10.0kA & PSC 10kA with light showing warning red triangle on touch metal plate on my fluke MFT ! Think I'm super close to a DNO supply transformer like 25 metres away max so would that get the Ze that low ?
Just went for a walk and found big transformer 20 metres away max as guessed & new batteries, leads, etc on mft but still 0.00
234 incoming so looking at it 234/0.00 is just the same : overflow on calculator or high estimate Fault current on tester ! Also used a 20kOhm resistor I have to check meter itself and it measured 20K spot on ! ...
This is always a problem by sub-stations and yes you would easily get 0.00. My meter reads to 3 digits, but it is qualified to within 6 digits in the manual so 0.002 could be 0.008 or.. less. Of course you cannot divide by 0 as you wind up with the original number. Also you must divide by 230 nominal voltage and multiply that by Cmin which comes out at 218.5 V./---. See Guidance Note 3. So if you can get a 3 digit ze reading then you may be able to do PFC calc. However that wont help as you will probably end up with massive Ka PFC i.e. .005=44Ka beyond any fuse capacity normally used domestically. As next year the 18th is bringing in 25mm tails/Main earth (I think) this is a problem that is going to get worse, not better.
Hi SS - yikes 0.00 ohms - If they've cabled it in 25/16 and it's say 30m effective, the OSG says about 0.056 ohms I think (noting bottle of red next to calc). To get 0.00 ohms result you'd need to be measuring a local short circuit - and you could get one of those if you were measuring N to E on TNCS perhaps? Quick check on polarity resulting from their connection of your new tails? Long shot, but it's all I got, sorry.
Edit - just read V's reply :)
How come you originally got 0.22.
I'm wondering if batteries in mft were getting tired as was down to 6.5V as opposed to around 9V in battery compartment before it runs through internal electronics etc.. some have posted erraneous results with low batteries. I tested some pipework with an R2 lead and got a high reading too then consistent lower readings afterwards, so wondered if sometimes mft behaves daft !
Maybe you should check in your manual the +- tolerances of measurement on Loop. i.e. mine is within 6 digits whats yours? And did they stick with TNS or change to TN-C-S?
Do you have L-PE and L-N switch on your test. And I always ask what the DNO reads on Cut out change for Ze. Maybe you could still ask them if they recorded it?
I do have those switchovers on the MFT Vortigern yes, & im hoping they did a test but doubt it ! Wondering if worth borrowing a Megger or similar and trying again !
Well I guess it certainly wont hurt you have to get a figure one way or another. But if your meter goes to 3 digits, you should get a measurement. I would phone the tech dept for your MFT and ask them what you can do, usually they are brilliant at helping out.
Are you a mind reader Vort ? Just had a call back from Erik in Netherlands (Fluke) he's saying always reset the zero / null memory when that happens as very likely that it's calculated extra resistance to deduct from what would already be a very low result. Makes sense as I sometimes have zeroed again between tests or after an on / off to be certain it's nulled the leads and is ready! Could well be operator error !
Also said always use the zero adaptor and never the probes touched together as because of far less surface area it will throw up silly small resistances and then you hit zero again to drop value and straight off you have a further deducted value ! He mentioned leads but I've tried a few so should be fine but again batteries on below self test should be careful below 8V as can throw up all kinds of results. Going to need shares in Duracell.
Old Megger 1553 wasn't so sensitive ! Prob my fault with zeroing though. Thanks to all of you guys :thumbsup::clapping:
Reply to Testing issues ! in the UK Electrical Forum area at ElectriciansForums.net
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...