Hi all,
bit of advice please - as the title, I have been asked to test a RFC which is served by a UPS. It's in an alarm receiving center. Any advice on what I need to watch out for, testing protocols etc? Not workred on this kind of set up before.

Regards.
 
If the rfc is fed by a UPS then in practice it is not part of the fixed wiring..As the ups output will not be connected to the input circuit in any way.

As it is NOT connected to the input I would think that the RFC should be treated as if it where being fed from an isolation transformer and treated accordingly !!?

I may be wrong though..................
 
Sounds reasonable to me. Totally isolated from the main system.

You say a data centre, so you need to start looking at the implications of an “isolated” earth returns within your “isolated” system.
 
Hi all,
bit of advice please - as the title, I have been asked to test a RFC which is served by a UPS. It's in an alarm receiving center. Any advice on what I need to watch out for, testing protocols etc? Not workred on this kind of set up before.

Regards.


Carry out your usual tests with the UPS in bypass mode.

When the inverter is in operation, the UPS itself will be factory set to clear any fault downstream, usually allowing a fault current to flow for around 100mS before automatically shutting down to protect the inverter.
 

Reply to Testing of an RFC linked to a UPS in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock