So I know this has been done to near death and different electricians have different ways/opinions on how to test an RCD. I was originally taught to test at the RCD itself, on the load side, with the MCB's switched off. Anyway, just recently I have had a few discussion/disagreements with a few other electricians regarding the actual test method to be applied. One said you had to test at any socket, the other said to test at the furthest point of the circuit.
Now I have read the GN3 and OSG on this matter and both seem quite inconclusive. The one thing that makes sense is when it states "as near as practical to the point of installation". So defo not the furthest point of the circuit! I have attached the paragraph's below. Each person I spoke to had a different view of what these paragraph's meant. So what do you think?

I have emailed a few manufacturer's as some people say that they advise to test "AT" the RCD itself as well. Below are the responses I got back from two of them.
Case number: 28307923
Dear XXXXXXXX
RCCB@s and RCBO's have a test button on the front that is used to test the unit.
To externally test the unit it may be possible to use a Plug tester or wire direct to the out going terminals.
Test method should be as detailed in the standard BS EN 61008 or BS EN 61009
At I delta n tripping 300mS
At 5x I delta n tripping 40mS
Kind Regards
Schneider Electric Advanced Technical Support
**Please only respond to this email if you have any further queries or information concerning the case referenced above.**
Thank you for your recent e-mail regarding your MK products.
Unfortunately we cannot give site specific installation/testing guidance, we suggest
that the RCD/RCBOs that you’ve described should be installed/tested to comply with the requirements of BS7671 (IET Wiring Regs) together with all relevant
associated guidance notes.
For any further clarification please call our help line on 01268 563720 and
one of our engineers would be happy to assist further with your query.
Assuring you of our best attention at all times. (E&OE)
Regards XXXXXX
Technical Sales & Service Department
MK Electric, The Arnold Centre, Paycocke Road, Basildon, Essex, SS14 3EA
This email and any attached files are confidential, protected by copyright and may be legally privileged
Your thoughts please guys. Is there any valid written proof of the correct test procedure for RCD?
Cheers
Jay
Now I have read the GN3 and OSG on this matter and both seem quite inconclusive. The one thing that makes sense is when it states "as near as practical to the point of installation". So defo not the furthest point of the circuit! I have attached the paragraph's below. Each person I spoke to had a different view of what these paragraph's meant. So what do you think?


I have emailed a few manufacturer's as some people say that they advise to test "AT" the RCD itself as well. Below are the responses I got back from two of them.
Case number: 28307923
Dear XXXXXXXX
RCCB@s and RCBO's have a test button on the front that is used to test the unit.
To externally test the unit it may be possible to use a Plug tester or wire direct to the out going terminals.
Test method should be as detailed in the standard BS EN 61008 or BS EN 61009
At I delta n tripping 300mS
At 5x I delta n tripping 40mS
Kind Regards
Schneider Electric Advanced Technical Support
**Please only respond to this email if you have any further queries or information concerning the case referenced above.**
Thank you for your recent e-mail regarding your MK products.
Unfortunately we cannot give site specific installation/testing guidance, we suggest
that the RCD/RCBOs that you’ve described should be installed/tested to comply with the requirements of BS7671 (IET Wiring Regs) together with all relevant
associated guidance notes.
For any further clarification please call our help line on 01268 563720 and
one of our engineers would be happy to assist further with your query.
Assuring you of our best attention at all times. (E&OE)
Regards XXXXXX
Technical Sales & Service Department
MK Electric, The Arnold Centre, Paycocke Road, Basildon, Essex, SS14 3EA
This email and any attached files are confidential, protected by copyright and may be legally privileged
Your thoughts please guys. Is there any valid written proof of the correct test procedure for RCD?
Cheers
Jay