SparkyMarky

:confused: Hello all,
I am a gas fitter and a domestic installer (limited scope) and was wondering what testing i have to do to install a spur (to fit a boiler) to a previously installed ring. Do i have to test the ring from the start as if i have installed it myself?
 
i would personally test the circuit your connecting into as you need to determine its condition, same as if you were connecting into an existing gas pipe. as well as fully testing your new circuit obviously, as well as checking the main bonding is in place to all incoming services. and the usual rcd protection etc.

hope that helps

rich
 
Thanks. it does!
Once you have tested the ring (including bonding Zs etc) would you then connect the spur into the ring and test from the spur as if it was just a spur originating from the consumer unit (ie connect line to eth at the consumer unit)
 

Reply to Testing spurs in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock