SparkyMarky

:confused: Hello all,
I am a gas fitter and a domestic installer (limited scope) and was wondering what testing i have to do to install a spur (to fit a boiler) to a previously installed ring. Do i have to test the ring from the start as if i have installed it myself?
 
i would personally test the circuit your connecting into as you need to determine its condition, same as if you were connecting into an existing gas pipe. as well as fully testing your new circuit obviously, as well as checking the main bonding is in place to all incoming services. and the usual rcd protection etc.

hope that helps

rich
 
Thanks. it does!
Once you have tested the ring (including bonding Zs etc) would you then connect the spur into the ring and test from the spur as if it was just a spur originating from the consumer unit (ie connect line to eth at the consumer unit)
 

Reply to Testing spurs in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
411
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
627
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
697
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
812
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
714

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock