Discuss tests on cu change in the Industrial Electricians' Talk area at ElectriciansForums.net
P
petewan
hi can you give me a bit of advice.
I'm changing a cu for a niceic registration job, do i have to test all of the installation as if it was a new installation.
I would be grateful for any advice you can give me
Thanks Pete
Its always a good idea to do all the tests as this would show up any problems with the existing install. Nothing worse than putting an RCD on everything and then having trouble through borrowed neutrals and the like.
Dont forget to ensure main bonding is in place too.
If you dont and he spots it, he will tear you a new one.
Besides, makes you feel better when you have done the tests and you have the results to give the customer. Its all about doing a good job.
To clarify, and support jasons post, you should do all the tests as you're changing the protective characteristics of every circuit. Also, make sure you do the tests before you start the CU change. You don't want to find any nasties in the installation and a customer saying "well they weren't there before you did your work". Obviously you'll need to do Zs when you're complete.
Hi there.
you HAVE to test everything.
when you change a consumer unit, YOU become resposible for the whole system. You sign the cert to say so!
hope this helps.
i cant see many people willing to pay for 2 tests to be done to their installation just for a fuseboard change, id personally jus make the client aware of what could possibly happen before carrying out the work. I can see your point of view though it would mean you would be out of pocket or time.
There is no need to do 2 tests on an install.
But, before i even consider ripping the old board of the wall i do IR tests to confirm circuits are sound.
Then, once the new CU is in place ill do the rest.
Job done.
don't need to do 2 tests. do all of the disconnected tests first on the initial DB. remove this DB, install new. you wont need to redo the IR, continuity, pol etc. do your PFC, RCD tests etc on the new board
so on and so forth
Reply to tests on cu change in the Industrial Electricians' Talk area at ElectriciansForums.net
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
NICEIC Certification Scheme Annual assessment
Hi I've seen posts on other forums suggesting that NICEIC will not accept a CU change for annual assessment unless accompanied by a new circuit...
Hi guys I’m at one of the funny times in my career where I can’t decide on what I want to do. I’m wondering if one of you experiences folks can...
Hi all, I am an electrician working for a OEM machinery manufacturer based in Germany, we are the local hub that is now taking over the...