This morning started with the plumber onsite rushing about trying to find a leak that was dripping from the newly plastered and painted ceiling in the corridor.

His pad saw came out and he started hacking away at the ceiling, he then started jumping about on his steps shout "I just got a shock"...
I thought...dont be daft.. theres only coax above the ceiling just there...

other trades soon gathered in the corridor to see what all the fuss was about.. So i got out my fluke volt stick and just touched the sides of the plasterboard and my stick shown it to be live...!!!

I then went across the surfice of the ceiling and it shown live about 5ft either side of the cut out plaster where the plumber had found his leaking copper joint..

Put my tester on the copper pipe work and that was not live, only the ceiling was live, even 10" down the timber door frame shown live!!

I new it was conducting through the water that was leaking, then spreading across the ceiling... I just couldnt figure out why... after alot of head scratching i decided to investigate in the ceiling.

It turned out to be a screw through the plasterboard on a traped cable....

Plasteres dont have a minute to live... goes to show bragging about the speed of your work doesnt mean a thing..


photo 2.JPG photo 1.JPG
 
Had very similar recently. Live wall, bloody joiner put a dildo rail up with nails directly above light switch. Took great pleasure in ripping freshly plastered and painted wall apart to fit new cable, then buggered off and left them the mess to sort out. I have come to the conclusion that most other "trades" are w888ers.

Cheers........Howard
 
Had very similar recently. Live wall, bloody joiner put a dildo rail up with nails directly above light switch. Took great pleasure in ripping freshly plastered and painted wall apart to fit new cable, then buggered off and left them the mess to sort out. I have come to the conclusion that most other "trades" are w888ers.

Cheers........Howard

What was it for mounting sex toys?

Think you mean DADO
 
My I/R test shown up 426 across L-PE, although this is low for a relitivley new install i didnt have much cause for concern as well within its limits.. This screw through the cable obviously shows now why i got this result

I'm also supprised the RCBO didnt trip..
 
My I/R test shown up 426 across L-PE, although this is low for a relitivley new install i didnt have much cause for concern as well within its limits.. This screw through the cable obviously shows now why i got this result

I'm also supprised the RCBO didnt trip..

At 426 Million Ohms, your RCD shouldn't be tripping.

It just goes to show how a very small amount of current can still cause a major scene, most 30mA RCD/RCBO's trip somewhere between 15 and 30mA.
 
At 426 Million Ohms, your RCD shouldn't be tripping.

It just goes to show how a very small amount of current can still cause a major scene, most 30mA RCD/RCBO's trip somewhere between 15 and 30mA.

I didn't expect it to trip due to I/R results, but I thought it was odd not to trip due to the imbalance from the current loss, I might even do a ramp test to see what it trips at.

Although for many this tingle that it was giving from the ceiling wasn't life threatening it could of had more serious effects from the fragile and elderly residents of the building.. It made me throw my hand back after touching ceiling anyway..!

I think it should have tripped and surprised it didn't
 
I didn't expect it to trip due to I/R results, but I thought it was odd not to trip due to the imbalance from the current loss, I might even do a ramp test to see what it trips at.

Although for many this tingle that it was giving from the ceiling wasn't life threatening it could of had more serious effects from the fragile and elderly residents of the building.. It made me throw my hand back after touching ceiling anyway..!

I think it should have tripped and surprised it didn't

With the poor conductivity of water, I'd bet you received a fair bit less than 10mA (The point at which you lose the 'let go' reflex).
 
What was the cable doing there in the first place?

This is where the cable loops off up to the upper light switch, the lengths of CLS where put in after my cable runs to lower the ceiling and then the day after it was boarded.
 