[FONT=&quot]I found this question in "practical giude to inspection, testing and certification" book

A lighting circuit is to be wired in l mm2 twin and earth thermoplastic [/FONT]
[FONT=&quot]cable, the circuit is protected by a 5 A BS 3036 fuse. What would be the [/FONT][FONT=&quot]maximum length of cable permissible to comply with the earth fault loop impedance requirements (Zs)? (Ze, is 0.45.)[/FONT]
 
it is how I did it
Zsmax for 5A 3036 is 9.58
[FONT=&quot]Ω
rule of thumb 9.58 * 0.75 = 7,17[/FONT]
[FONT=&quot]Ω
[/FONT]
[FONT=&quot]Zsmax - [/FONT][FONT=&quot]Ze[/FONT][FONT=&quot] =
7,17[/FONT]
[FONT=&quot]Ω[/FONT] - 0.45 [FONT=&quot]Ω[/FONT] = 6.72 [FONT=&quot]Ω[/FONT]
[FONT=&quot]R1+R2 = 36,20 m[/FONT]
[FONT=&quot]Ω/m

Length * (R1+R2)/1000 = 6,72
[/FONT] [FONT=&quot]Ω[/FONT][FONT=&quot]
lenght = 185 meter

I try to prepare myself to C&G2391 exam but it is very difficult as I have to use a book with so many errors.
According to Practical Guide to Inspection Testing and Certification the answer is 498meters (this is one of many errors in this book)
thanks a lot I just needed somebody to confirm my calculation
[/FONT]
 
looks like they used the max zs value of 100% of 17.7 ohms for the 5 second disconnection time .
remember the .8 rule is only to give us a safety margin, not the max zs allowed.
 

Reply to the maximum length of cable permissible in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
764
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hi I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs. In some cases where there is no RCD protection the length is...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock