If the incomer is the bottom one, with the earth attached, then that's pretty normal for old earthing by the dno.
They are obliged to provide and maintain the earth only if it was there previously, as it is, there is an earth; so they comply with their obligations.
I would fit the new cu as normal but add a MET with 16mm^2 between the cu and MET, and a 10mm^2 between the MET and the existing bond where it connects to the cable incomer, and connect the twin 7/44 to the MET.
That way your (customer's) side is in every way compliant, you could also contact the dno and say you don't believe their existing earthing is being maintained properly as it is high resistance, they may follow up and fit a newer earth connection between your MET and their cable.
You could use the poor arrangements associated with the shared/interlinked supply to get them there.