Hi, i'm a little confused about the way to calculate the amp of the circuit breaker for a three-phase system.

If i have a power of 11.5 kW and voltage of 400V, what size circuit breaker is needed for three-phase system.

My calculation was 11500/(1.732x400) = 16.6 Amps per phase ... 16.6 x 3 = 49.8 Amps, so i need a 50 Amp breaker.

Please, tell me if i worked this out correctly, if not show me how it should be calculated and state the required circuit breaker size i need.

Thanks in advance.
 
why did you multiply 16.6 x 3 again?

a three phase circuit breaker will have 3 x MCB's linked at the switch (most likely)
 
Last edited:
I would have thought the 16.6 is in amps per phase so if there are a total of three phases you have to multiply it by three ? (This is what was confusing me)

There are not going to be individual circuit breakers, just the one.
 
One of the biggest benefits of three phase is that we can lower the circuit demand of higher rated equipment.
 
Last edited:
So, your saying a three-phase circuit breaker say 32 amp is actually 3x32amp MCBs fitted together?
 
So, your saying a three-phase circuit breaker say 32 amp is actually 3x32amp MCBs fitted together?

A basic 3 phase MCB is 3 single MCB's, formed together with a link to ensure isolation of all Live conductors occurs. More specific, higher rated MCB's will be specially manufactured.
 
Okay, i understand but, just to make sure your saying in reference to my calculation in my original post, a 20 Amp breaker would be enough?
 
Correct,

11500w on single phase = 11500/230 = 50Amp
11500w on three phase = 11500/√3 x 400 = 16.60Amps, so a 20Amp MCB should suffice (assuming no inrush or anything to be considered).
 
Is this for a motor? If so you may have to consider a 32A type C and cable accordingly.
 
Last edited by a moderator:
It's an air compressor in a workshop, it wasn't a balanced load i.e. it required a neutral as well.
Origanally, i had used a 32 Amp type C but, it tripped instantly afterwards, i was told it requires a 50Amp breaker type C, which worked.
I'm not sure how 50Amp was calculated, the only way that made sense to me was to multiply by 3 (refer to original post), and this is where my confusion is.

Thanks for the replys, i hope you can clear my mind on this one.
 
It is a very big compressor and it is very likely you may be right about it being per phase.
I will make sure to check it again to confirm, thanks.
 
Last edited by a moderator:
ta I have to assume that as it's a large compressor it is star-delta connected, When you say you fitted a 32amp C breaker and it tripped have you connected it right ie star-delta, because if you haven't and connected to the wrong contactor so it is delta-star it would easily trip.

If you have connected it correctly is the star-delta timer an adjustable one, again if it is then you could be running on star start up to long, so look at that, or even look at a faulty timer.

Finally as widdler suggest is it 11.5kw per phase which in pit terminology make it a FBC ............... F big compressor.
 
i can't see the motor being 11.5kw /phase. the fact that a 32A C is tripping leads me to believe that the motor is goosed.
 
@malcolm, yes it is star-delta and i would assume it is connected correctly otherwise the 50Amp breaker would not have worked either. I haven't confirmed whether it is 11kW per phase but, will do so soon as well as checking the timer.

@telectrix, sorry can you elaborate on what you meant when you said 'goosed'? Thanks.
 