It depends on the earthing system, and the tape of circuit the RCD is protecting.
Distribution circuits and final circuits 32A and greater, 5 secs, unless it's a TT installation, when it's 1 sec.
Final circuits less than 32A, 0.4 secs and 0.2 secs for TT.
 
Hi guys
Quick question
Does anyone know the max trip time for a 100mA time delayed RCD
Max 500ms min 130ms
No good being 2 seconds as max disconnection times on a TT are 0.2 seconds and 1 second
Max resistance of Ra would be 500 ohms before 50v touch voltage is exceeded.
50/0.1 = 500 ohms for 100 mA rcd.
 
Last edited:
Spinlondon has described the maximum tripping times for circuits that are protected by ADS with an RCD. The circuits would also need overcurrent protection.
Ian1981 has described the trip times for the RCD as a item in its own right irrespective of its circuit connections.
Your trip time of 443ms would meet the requirements for the device as an RCD but would not meet the requirements for disconnection time for a final circuit on a TT system.
 
Spinlondon has described the maximum tripping times for circuits that are protected by ADS with an RCD. The circuits would also need overcurrent protection.
Ian1981 has described the trip times for the RCD as a item in its own right irrespective of its circuit connections.
Your trip time of 443ms would meet the requirements for the device as an RCD but would not meet the requirements for disconnection time for a final circuit on a TT system.
If it is only a 1 second disconnect time required then it will comply as it will trip with in 0.443 of a second.
 
If it is only a 1 second disconnect time required then it will comply as it will trip with in 0.443 of a second.
Sorry you said fi
The 100mA has being used upfront and a dual RCD board has being fitted with obviously 30mA protection for all final circuits.
If it's a metal consumer unit the 100mA will protect the internal link tails incase they short out to the metal case so will comply as it will be a 1 second disconnection time required
 
I'm confused, easily done.

A S Type Time delay RCD, to BS EN 61008-1 or 61009-1, trip times are 130 minimum to 500 maximum (ms), as per Table 3A. It cannot be adjusted, it does what it says (on the tin). So why are we discussing which circuits to put it on?
 
A time delay is ok for circuits with a 1 second disconnect time only on tt.
So circuits up to 32amps has to be 0.2 seconds disconnect time so if the rcd tripped above 200ms then although the rcd satisfies manufacturers times it won't satisfy the 0.2 disconnect time required for the circuit.
 
Hmmm, understand that. I also understand sockets, cables in wall less than 50mm etc etc, require 30mA RCD. I also note the use of 30omA RCD for fire protection, etc. An S Type 100mA has only one use?
 
Hmmm, understand that. I also understand sockets, cables in wall less than 50mm etc etc, require 30mA RCD. I also note the use of 30omA RCD for fire protection, etc. An S Type 100mA has only one use?
The time delay is purely protecting the internal tail links in the metal consumer unit.
The consumer unit has 2 30mA rcds in it as stated by the OP I think.
So using a time delay 100mA on a domestic split load board in place of main switch.

Is that what you mean or i may be babbling?
 
The time delay is purely protecting the internal tail links in the metal consumer unit.
The consumer unit has 2 30mA rcds in it as stated by the OP I think.
So using a time delay 100mA on a domestic split load board in place of main switch.

Is that what you mean or i may be babbling?

Pretty much; S Type can only be used for a distribution circuit, although I might be wrong? OP was just asking for min/max times of S Type.
 
Time delayed RCDs are used for discrimination.
If the upfront RCD was not time delay, then a fault which would cause a downstream device to trip would most likely also cause the upfront RCD to trip.
Might as well only have the one RCD for the whole installation.
 

Reply to Time delayed 100mA RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to put a code pad via a time delay relay on a shutter door, any recommendations?
Replies
7
Views
558
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
877
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
849
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
280

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock