Hi darkwood,
I can only go from past experience, I was part of a crew installing basic electrics in about 30 small factory units (100A per phase), this work consisted of a single 32A TP+N socket for general use, another TP+N socket at height for the roller/up and over door, two 32A TP+N Isolators, and several SP sockets dotted around for general use, and the guy in charge stipulated all SP sockets to be on the same phase in the workshop area (for the reason I gave earlier), and all SP sockets in other rooms/parts of the unit on the same phase(but different to the workshop area).
The SP sockets were still balanced across 3 phases, ie. workshop on one, office on another, reception and toilets etc. on the other.
All lighting in the workshop to be on staggered phases (different phase per bank).
I did not find a reg to say this was the way it had to be done, but the guy in charge obviously knew his stuff as he was the project manager for the whole estate, so who am I to argue.