Now that is much easier said that done!!!
God knows how I'm going to manage that.
It's all concrete floors and laminate flooring with the DB in the middle of the house.
The house has been extended many times in an outward direction from the DB and their is no accessible avenues left to it.
I think I really need to explain all this to the customer before I do anything else.
There's a good chance, that it's not TN-S.
Looks like a split concentric cable, and it appears that both the neutral and earth conductors have been terminated in the neutral block.
I'd consider removing the clamp, and terminating the earth in the neutral block.
There's a good chance, that it's not TN-S.
Looks like a split concentric cable, and it appears that both the neutral and earth conductors have been terminated in the neutral block.
I'd consider removing the clamp, and terminating the earth in the neutral block.
I've never dealt with DNO's, but can't he call them to upgrade the meter to a digital one, (done free round here last couple of years) and install an isolator at the same time? or is this just showing my ignorance??
It will have been TN-S, it’s a paper lead cable. The give away is the way the cable crotch is taped, that’s not a new fangled heat shrink termination. As I said in a previous post for gods sake DO NOT play about with it. The separate L / N blocks are typical of early 50’s supplies. My first house had them.