A wholesaler tried to tell me that Surge protection is now a requirement in DBs under 18th Regs today. Im pretty sure thats rubbish but just wanted to put it out there. I know alots been added on SP in the new Regs but Im pretty sure its still only risk assessment driven and not a requirement in a single dwelling where cost out ways potential loss. They also tried telling me that surge protection from lightning is required, but I'm fairly sure that theres a probability calc for lightning (if anyone can remind me of it that would be great!) that I did on a design course a few years ago that proved that lightning in this country wasn't frequent enough to warrant a 'SP protection needed' outcome of the calc.

Cheers chaps

Spud
 
Hi,

A wholesaler tried to tell me that Surge protection is now a requirement in DBs under 18th Regs today. Im pretty sure thats rubbish but just wanted to put it out there. I know alots been added on SP in the new Regs but Im pretty sure its still only risk assessment driven and not a requirement in a single dwelling where cost out ways potential loss. They also tried telling me that surge protection from lightning is required, but I'm fairly sure that theres a probability calc for lightning (if anyone can remind me of it that would be great!) that I did on a design course a few years ago that proved that lightning in this country wasn't frequent enough to warrant a 'SP protection needed' outcome of the calc.

Cheers chaps

Spud
Trying it on Spud trying to up his profits
 
I believe there is an exemption you can use for single household domestic properties, but that aside you either fit it or carry out a risk assessment and make a decision based on that.
 
443.4 Overvoltage Control

Protection against transient overvoltages shall be provided where the consequence caused by overvoltage could:

(i) result in serious injury to, or loss of, human life, or
(ii) result in interruption of public services and/or damage to cultural heritage, or
(iii) result in interruption of commercial or industrial activity, or
(iv) affect a large number of co-located individuals.

For all other cases, a risk assessment according to Regulation 443.5 shall be performed in order to determine if protection against transient overvoltages is required. If the risk assessment is not performed, the electrical installation shall be provided with protection against transient overvoltages, except for single dwelling units where the total value of the installation and equipment therein does not justify such protection.
 
I believe there is an exemption you can use for single household domestic properties, but that aside you either fit it or carry out a risk assessment and make a decision based on that.
Where Surge protection may not be required
Protection against over voltages of atmospheric origins not required in the following circumstances but the rated withstand voltage of equipment must meet the requirements of Table 443.2 of BS 7671:2018

Where SPD protection is required
Protection against Transient over voltages shall be provided where the consequence caused by over voltage:
a) Results in serious injury to, or loss of life e,g, ( Hospitals , Care homes , home dialysis equipment.
b)results in interruption of public services and/or damage to cultural heritage,e,g (data centers, heritage status buildings like museums and castles)
c) results in interruption of commercial or industrial activity e,g, ( banks, hotels, supermarkets, industrial plants, farms)
d) affect a large number of collocated individuals e,g, ( offices, universities, schools residential tower blocks)

For all other cases than above a risk assessment to determine the Calculated Risk Level CRL shall be conducted to 443.5 (See appendix IET gn 1 for further info)
 
No CRL risk assessment required for single dwellings, just whether it justifies protection for the equipment Thein ie cost.
If the dwelling has say a life saving machine in it like a dialysis machine or other health/life support equipment for treatment at home, then that could come under indent (i) loss of life so it will most likely be required
 
Where Surge protection may not be required
Protection against over voltages of atmospheric origins not required in the following circumstances but the rated withstand voltage of equipment must meet the requirements of Table 443.2 of BS 7671:2018

Where SPD protection is required
Protection against Transient over voltages shall be provided where the consequence caused by over voltage:
a) Results in serious injury to, or loss of life e,g, ( Hospitals , Care homes , home dialysis equipment.
b)results in interruption of public services and/or damage to cultural heritage,e,g (data centers, heritage status buildings like museums and castles)
c) results in interruption of commercial or industrial activity e,g, ( banks, hotels, supermarkets, industrial plants, farms)
d) affect a large number of collocated individuals e,g, ( offices, universities, schools residential tower blocks)

For all other cases than above a risk assessment to determine the Calculated Risk Level CRL shall be conducted to 443.5 (See appendix IET gn 1 for further info)
The missing bit
Where SPD may not be required
For single dwelling units where the total value of the installation therein, does not justify such protection and the consequential losses are tolerable
To be read as "Where SPDs may not be required"
Page 39 18th edition
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

spud1

Arms
-
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
To Surge protect or not Surge protect that is the Question!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
31
Unsolved
--

Advert

Thread statistics

Created
spud1,
Last reply from
Nebu1a,
Replies
31
Views
15,112

Advert

Back
Top