I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks
 
around that time it was usual to fit an up front 100mA RCD on a TT system. if you are doing any work in it, i'd be inclined to fit a new CU with 100mA delay RCD as main switch and 30mA RCD/RCBOs for all circuits.
 
I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks

If it had RCBO,s this would give you your RCD protection would it not ?, unless you meant MCBs ?
 
Ah! right MDJ,

I read it as there were only a few circuits, (all) with RCBO protection, cheers,

In that case ^^^ what Tel said
 
"Shall we eat grandma?"
"Shall we eat, grandma?"

Big difference. ;)

One day... One day, I will have summat useful to contribute other than inanities.
 
I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks

What was the Ra?
 
Its been 22 minutes since your post. Did you eat Grandma??

Om nom nom... :)

grandmother.jpg
 
Last edited:
What was the Ra?


A very important question, when considering this is an industrial installation.

Still amazes me just how little many sparks know about TT systems, especially when talking about industrial and medium to large commercial applications....
 