I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks
 
around that time it was usual to fit an up front 100mA RCD on a TT system. if you are doing any work in it, i'd be inclined to fit a new CU with 100mA delay RCD as main switch and 30mA RCD/RCBOs for all circuits.
 
I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks

If it had RCBO,s this would give you your RCD protection would it not ?, unless you meant MCBs ?
 
"Shall we eat grandma?"
"Shall we eat, grandma?"

Big difference. ;)

One day... One day, I will have summat useful to contribute other than inanities.
 
I was doing work on an commercial site today. The supply is TT and the install is about 25 years old. I was under the impression a TT system had to be RCD protected to meet disconnection times. But this install only had a few circuits with RCBO's. Would the version of regs the install was designed to not require RCD protection? Thanks

What was the Ra?
 
Its been 22 minutes since your post. Did you eat Grandma??

Om nom nom... :)

grandmother.jpg
 
Last edited:

Reply to TT and RCD Protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
772
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
731
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock