no. the 30mA RCD is for all final circuits, not distribution circuits. it's the fault protection that protects SWA form damage. in this case an RCD is used on TT systems as the EFLI is too high to achieve disconnection times, generally 5 secs. for a dist. cct.

That's really helpful.

Cheers
 
Hi, a bit of advice required. I need to install another d.b to a garage, the tails are to be split. The earthing system is TT, the cable is armoured, clipped to the side of the building & over to the garage on a small cantenary wire. As it is TT would the distribution cable need to have rcd protection? I have been told it doesn't, but the regs stipulate 1 second disconnection time.

Cheers
depending on over current protection i think you find it 0.2 sec
 
distribution circuit, 1 sec. (see 411.3.2.4.) it's 0.2 secs. for finals.
 