Discuss TT distribution circuit in the UK Electrical Forum area at ElectriciansForums.net
soulman
Hi, a bit of advice required. I need to install another d.b to a garage, the tails are to be split. The earthing system is TT, the cable is armoured, clipped to the side of the building & over to the garage on a small cantenary wire. As it is TT would the distribution cable need to have rcd protection? I have been told it doesn't, but the regs stipulate 1 second disconnection time.
Cheers
bit you'll need the RCD for fault protection to achieve your disconnection time.
I would put a 100ma type s (time delayed) then your switched fuse to protect your distribution circuit. Then 30ma RCDs to cover circuits from 2nd DB.
Thanks for advice, much appreciated,
I was going to use a 100ma as the cable was clipped, i would have used 30ma if cable was buried.
why use 30mA for buried cable - mole protection?
you are using an SWA...so this cable type enjoyes an earthed metallic covering yes...
so no need for the 30mA for it...and dont forget as well if you gave the SWA 30mA top end for fault protection...then how are you going to split the finals and acheave discrimination & diversity?..
got to think these things through mate ....
I always thought 30ma had to be used when buried on TT, incase someone cut through the cable. Thanks for that appreciated.
no. the 30mA RCD is for all final circuits, not distribution circuits. it's the fault protection that protects SWA form damage. in this case an RCD is used on TT systems as the EFLI is too high to achieve disconnection times, generally 5 secs. for a dist. cct.
and finals over 32A...which begs me to ask after looking at a recent condition report carried out by a so called `competant person`...he had put 63A OPDs down as .4
as well as a multitude of other made up crap..
well i guess you sees stuff every day....
That's really helpful.
Cheers
Cheers
depending on over current protection i think you find it 0.2 sec
distribution circuit, 1 sec. (see 411.3.2.4.) it's 0.2 secs. for finals.
Reply to TT distribution circuit in the UK Electrical Forum area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
4K
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...