If that's the case then these breakers do not comply with BS 3871 Type 4 breakers. That is the whole point of having a BS typing for MCB's!!

Well, in this case i still am better off using the manufacturers data rather than comparison with a type d 3871. I have recommended a rolling plan of board changes, which is going to take a few years, but atleast i have done everything in my power to have the correct information to put down. At the end of the day, they pass according to manufacturers data, which atleast explains why they were put in in the first place. Now down to them.
 
The times i have are different to those, even with rule of thumb.. can i ask where you got this info?
 
Well, in this case i still am better off using the manufacturers data rather than comparison with a type d 3871. I have recommended a rolling plan of board changes, which is going to take a few years, but atleast i have done everything in my power to have the correct information to put down. At the end of the day, they pass according to manufacturers data, which atleast explains why they were put in in the first place. Now down to them.

How can manufactures data of MCB's marked up as ''Type 4'' differ from those set out in the British Type 4 Standard for god's sake?? You have a minimum and maximum tripping time/current characteristic where the maximum is generally taken for Zs purposes. MCB's are manufactured to meet a specific trip Type, under British standards, Not the other way round!!

Changing these DB's is a good plan, Personally i wouldn't even a thank You for any of those old Yank based Fed Elec board or breakers
 
How can manufactures data of MCB's marked up as ''Type 4'' differ from those set out in the British Type 4 Standard for god's sake?? You have a minimum and maximum tripping time/current characteristic where the maximum is generally taken for Zs purposes. MCB's are manufactured to meet a specific trip Type, under British standards, Not the other way round!!

I for one did not install these boards, nor am i advocating their use. They are installed.. there are hundreds of them, and all i can do is show the data that i have and suggest a recommendation. Either way, the data states that the breakers are tested to certain standard. Are you saying that on a test sheet i should NOT put down the manufacturers data? I would question that.
 
How can manufactures data of MCB's marked up as ''Type 4'' differ from those set out in the British Type 4 Standard for god's sake?? You have a minimum and maximum tripping time/current characteristic where the maximum is generally taken for Zs purposes. MCB's are manufactured to meet a specific trip Type, under British standards, Not the other way round!!

I for one did not install these boards, nor am i advocating their use. They are installed.. there are hundreds of them, and all i can do is show the data that i have and suggest a recommendation. Either way, the data states that the breakers are tested to certain standard. Are you saying that on a test sheet i should NOT put down the manufacturers data? I would question that.

I'm not blaming you in any way shape or form for the installation of these panels and breakers. What i am saying is that if the manufactures data differs from those of the appropriate BS for Type 4 MCB's then they ain't bona fide Type 4 breakers. The ''certain standard'' you mention above does not conform to the Type 4 breakers of that time, it's as simple as that!!

And as i stated above, changing these panels and breakers over a certain given period of time is about the best action you can or could take in this situation!!
 