How can manufactures data of MCB's marked up as ''Type 4'' differ from those set out in the British Type 4 Standard for god's sake?? You have a minimum and maximum tripping time/current characteristic where the maximum is generally taken for Zs purposes. MCB's are manufactured to meet a specific trip Type, under British standards, Not the other way round!!
I for one did not install these boards, nor am i advocating their use. They are installed.. there are hundreds of them, and all i can do is show the data that i have and suggest a recommendation. Either way, the data states that the breakers are tested to certain standard. Are you saying that on a test sheet i should NOT put down the manufacturers data? I would question that.
I'm not blaming you in any way shape or form for the installation of these panels and breakers. What i am saying is that if the manufactures data differs from those of the appropriate BS for Type 4 MCB's then they ain't bona fide Type 4 breakers. The ''certain standard'' you mention above does not conform to the Type 4 breakers of that time, it's as simple as that!!
And as i stated above, changing these panels and breakers over a certain given period of time is about the best action you can or could take in this situation!!