Well that was interesting. Is that actually saying that it is incorrect to test a x5 on the 30mA setting (i.e. 150mA) and saying that we should be testing a 30mA RCD on the 300mA setting in order to make sure it is tripping within 40mS at x 5?
 
Aico 3000
This official sponsor may provide discounts for members
Hager devices are manufactured to disconnect within 40ms with a test current of 250ma, this is obviously above the ×5 we are accustomed to testing at but is inline with EN61008.
Regulation 643.8 does not specify a precise ×5 test current, it states ×5 or above which takes into account this 250ma. Personally to me if it trips within requirements at ×5 then it is fine.
 

AJshep

-
Esteemed
Arms
The early Hager guidance of testing their A type RCDs was a bit of a cop out in my opinion. Westwood sums it up in his post above.
Never understood why everyone else could make a 30mA type A RCD trip at 30ms at 150mA but Hager couldn't.

At least they seem to have brought their devices inline with everyone else now.
 