I heard a rumour that cutting moulded plugs off invalidates your car insurance and stunts the growth of any veggies your growing in your garden. :biggrin:
what's car insurance? and we don't have plumbers or kitchen fitters growing in our garden.
I heard a rumour that cutting moulded plugs off invalidates your car insurance and stunts the growth of any veggies your growing in your garden. :biggrin:
might only need an additional cpc ....parralleled up with the existing one in the cable..........An RCD may be classed as either additional protection or to satisfy disconnection times....411.4.9.
If in the case of the OP if it was found that starting surges were a problem with a type B...and the Zs exceeded the maximum allowable for a type C OCPD would you rewire the circuit in a larger cable to bring it within the allowances for a type C..??,(or some other expensive fix?), when the regulations permit the RCD element of the device already installed to meet the requirements for disconnection times?
If you prefer the first option I'm glad I'm not one of your cutomers.
4mm??...bad cable to use nick mate as dont forget....still only a 1.5mm cpc..........I'd be inclined to go with glen sparks point and run in a radial but i would run it in a 4 or 6mm only reason is the cpc is larger in these so there fore the Zs readings should be lower i am a big fan of keeping the Zs as low as possible ,and for reasons eng54 has stated RCD's do fail , for certain circumstances you can install sockets without RCD protection
No it's a spur off a radial.
An RCD'd spur off a radial.
if its an addition or an alteration to an existing circuit then its a minor works ......if in a garage (remote or attached as in this case) then it isn`t notifyable....
An RCD may be classed as either additional protection or to satisfy disconnection times....411.4.9.
If in the case of the OP if it was found that starting surges were a problem with a type B...and the Zs exceeded the maximum allowable for a type C OCPD would you rewire the circuit in a larger cable to bring it within the allowances for a type C..??,(or some other expensive fix?), when the regulations permit the RCD element of the device already installed to meet the requirements for disconnection times?
If you prefer the first option I'm glad I'm not one of your cutomers.
You can get RCD'd FCU, if you attached one to the end of a radial would it then be notifiable?
So its a new circuit, and thus its notifiable.
That's how I see it.
It's an extension of a radial which is fused at 32 Amps in the house.